Hi Everyone, I need some guidance on reading/working on ladder diagram.
Was trying to read a program in TIA 15 but there is a network below which I could not find where the coil is or what actually activating the contacts. I tried to searh the whole program but did not come up with anything.

---||------------------------(Q4.0)---

The contact is M100.3 but I checked all cross referenced networks and run a search but could not locate what activates M100.3.

Is there a way that this is hidden or maybe programmed in a different way?
  Reply With Quote
Unread September 15th, 2019, 02:53 AM   #2
Lare
Member
Finland

Lare is offline
 
Join Date: Jan 2006
Location: Finland
Posts: 1,166
M-merker use same memory area than MW, and MD.
Check if MW100 is used somewhere on the program.


It is also possible that M100.3 is indectly addressed or even setted from HMI or scada directly.
  Reply With Quote
Unread September 15th, 2019, 03:01 AM   #3
franchois13
Member
France

franchois13 is offline
 
Join Date: Nov 2008
Location: london
Posts: 76
Quote:
Originally Posted by Lare View Post
M-merker use same memory area than MW, and MD.
Check if MW100 is used somewhere on the program.


It is also possible that M100.3 is indectly addressed or even setted from HMI or scada directly.
Machine is not controlled by HMI/scada so I will take that option out. Will double check again MW and MD as you mentioned.
How can I find out if it is inderectly addressed?
Thanks.
  Reply With Quote
Unread September 15th, 2019, 05:41 AM   #4
cardosocea
Member
United Kingdom

cardosocea is online now
 
Join Date: Nov 2016
Location: Fields of corn
Posts: 1,445
I don't think you can find if it is indirectly addressed really. :/



What does Q4.0 actually do? What is connected to it?



Thinking about it, there is another possibility which would be that the clock bit was configured in Byte 100 and Q4.0 is pulsing (either as a heartbeat or something else). Where is this rung located? and does the rung always process or does it have a jump to skip it or the function it is in?

I doubt it's this situation, but could happen.
  Reply With Quote
Unread September 15th, 2019, 05:55 AM   #5
franchois13
Member
France

franchois13 is offline
 
Join Date: Nov 2008
Location: london
Posts: 76
Quote:
Originally Posted by cardosocea View Post
I don't think you can find if it is indirectly addressed really. :/



What does Q4.0 actually do? What is connected to it?



Thinking about it, there is another possibility which would be that the clock bit was configured in Byte 100 and Q4.0 is pulsing (either as a heartbeat or something else). Where is this rung located? and does the rung always process or does it have a jump to skip it or the function it is in?

I doubt it's this situation, but could happen.
Q4.0 is driving a run relay for inverter which is driving a machine infeed conveyor so it is actually operating quite frequent as the machine starts and stops. The rung is located in one of the FCs.

Last edited by franchois13; September 15th, 2019 at 06:06 AM.
  Reply With Quote
Unread September 15th, 2019, 10:35 PM   #6
Mike Lamond
Member
United States

Mike Lamond is offline
 
Join Date: Oct 2009
Location: Syracuse, NY
Posts: 80
Quote:
Originally Posted by Lare View Post
M-merker use same memory area than MW, and MD.
Check if MW100 is used somewhere on the program.


It is also possible that M100.3 is indectly addressed or even setted from HMI or scada directly.
I have worked on other vendors' programs where one word was used to control a reversing starter, with bit 0 driving the forward output and bit 1 driving the reversing output. The program wrote 0 to the word at the beginning of the program, then several sections wrote 1 for forward or 2 for reverse when the logic was true. The cycle logic permitted only one section at a time to control the motor.

My preference would be to have a rung for each coil with branches for the output logic from each section. I consider this much better practice and far easier to troubleshoot.

Mike
  Reply With Quote
Unread September 16th, 2019, 02:16 AM   #7
cardosocea
Member
United Kingdom

cardosocea is online now
 
Join Date: Nov 2016
Location: Fields of corn
Posts: 1,445
Do you see any logic anywhere written in STL? Usually pointers are easier or only possible to assemble in STL. So that would be an indication.

Is there a network connection to another PLC, perhaps? That would explain why you don't see M100 being written.

Can't think of much more without seeing the program. :/
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
PLC ladder diagram using Rslogix 500 ( Micrologix 1500 Allen Bradley) Questor22 LIVE PLC Questions And Answers 4 March 18th, 2014 02:07 AM
Doubt in PLC ladder logic inputs usage gandhi LIVE PLC Questions And Answers 2 August 17th, 2010 06:57 AM
OEM PLC / microprocessor with ladder programming johnyu LIVE PLC Questions And Answers 6 July 26th, 2010 02:18 PM
Mitsubishi PLC : How to enable hidden ladder zai_jnr LIVE PLC Questions And Answers 4 February 20th, 2010 09:36 AM
Real World Problem Vietnam Bob LIVE PLC Questions And Answers 8 November 23rd, 2002 02:03 PM


All times are GMT -5. The time now is 04:45 AM.


.