how to chose transmitter for plc
vikas1947
Jun 2011
india
172
i have a pt 100 temprature sensor it have three wire 2 white and 1 red ,,i asked to alen Bradly support people about wiring they said me to buy a transmitter for my RTD which can convert its resistance in voltage or current ..
now I have a ml1100 which have two analog input port and one common port for both of them .....
its input value is given in 0 to 10 volt in the manual ...
when i went to market i asked for RTD transmitter he told me about 4-20 mA 0-20 mA 0-10 volt type of transmitter
suggest me which type i have to buy and why i have to buy that particular type :rolleyes:
I HAVE CAT NO. OF PLC 1763 L16BBB
The RTD transmitter itself is only part of the cost.
The 0-10V output of the RTD represents some temperature range, say, 0-100°C.
If the factory default range is not correct for what you need, then the range needs to be changed, typically with PC software and a modem/cable device. Depending on brand and model, that PC software and modem/cable can range from free to $5,000 USD.
If this is a one time deal, you might consider buying an RTD transmitter whose software/modem is free or from a vendor who will range it for you, so that you do not have to invest in software and a modem for a one-time range operation.
Good Practice is to put an adhesive label on the RTD transmitter with its range.
Hi every body i m doing electrical engg (specialization in Electronics) i wana do PLC based project i need help to chose final year project plz...
2,928
Does anyone have experience wiring this type of analog pressure transmitter up? It's 4 wires. 3 blacks and 1 green which I assume is earth...
298
I need to protect some pressure transmitters from hot (120°C) oil. Does anyone have a favorite transmitter cooling element/standoff they use...
180
Hi ,when i check the 4-20 ma output from flowtransmitter with multimeter ,it can shows 4 ma , but when i check with process meter it only shows...
169
How fail safe mode in level transmitter works? customer requesting for fail safe mode when the transmitter got any issue or power loss on the...
1,012