Post subject: Mitsubishi PLC RS485 2W Communication to Weintek HMI..

Ray_Z

Member
Join Date
Dec 2014
Location
Lahore
Posts
5
We have two PLCs both are Mitsubishi-FX2N, and we want them to communicate to Weintek HMI MT8100ie.
MT8100ie can communicate with Multiple PLC and it Supports RS232 on Com1, RS485 (2W/4W) on COM1 and RS485 (2W only) on Com3.

So, we are using RS232 on COM1 for PLC1 and COM3 (RS485 2W) for PLC2.

PLC1 is successfully communicating over RS232 Com1 (after a RS422 to RS232 converter), but PLC2 is not. :oops:

What i have known Mitsubishi has RS422 default and its 4 wired. :whistle: Its our limitation we cant use 4w we are left with 2w mode.

We tried different Parameters and wiring but still we are unable to get anything.

Any help / Guidance in this regard will be highly appreciated.
 
With the Weintek you can only choose one port or the other. If you are using RS232 that is only for a single point communication between two devices. Not only that but RS232 requires 3 wire for read write communication. The Weintek can communicate with multiple PLC's But only in the RS485 mode where each PLC is addressable.
 

Similar Topics

Hello All, Please direct me to post to the right page. I am really new to PLC, and want to find a tutor who is familiar with Automation Direct's...
Replies
9
Views
412
I know it is fairly simple to post a screenshot, but many of us have large screens, so perhaps y'all could take the time to trim those screenshots...
Replies
4
Views
526
Good day all. Stupid question incoming (see my handle), but I can't seem to get this last step sorted. Basic story: Ops ruined the PC we were...
Replies
4
Views
759
We are experiencing VM OS corruption after Studio 5000 installation. This has occurred for several VMs. Strangely enough, not every VM is...
Replies
3
Views
1,414
Hi I’m struggling to understand how the LHTTP_post / get work ? I have a url address given to me by the IT , I have to send a works order...
Replies
2
Views
1,242
Back
Top Bottom