to PID or not to PID that is the question
rscott9399
Aug 2017
in space
114
Hypothetical
You have an oil pump running.
You are reading a flow in GPM that is properly spanned from the device on a 4-20.
You need to add an additive to the flow. There is no flow meter on that additive so all you can do is turn the additive pump speed up and down with a 4-20 output. An operator will simply adjust on a 0 - 100% scale how fast the additive pump runs in relation to the flow.
The pump speed must be proportional to the flow.
I can do this easily with a bunch of compute statements and it turns into a math exercise.
Question : is simply doing the math the best option or is there an easy way to do it with a PID block in one rung?
any thoughts?
You can't have a PID without a process variable. What is the feedback that the PID would be adjusting to?
If you just need the pump speed to be proportional to the flow, a calculation is the only way to do that.
As i said above, i have a process variable.
I can use the oil flow as feedback.
So obviously not typical but im curious if there is a simple way instead of the math statements
You do not have a feedback. You are looking the concentration of an additive but have no way of measuring that additive, therefore it is open loop and math is the way to go.
i do have A A A A feedback lol just not feedback of the pump i want to control
alright, will scrap that idea
Math it is
thanks for the ideas
No you do not have a feedback, you have a setpoint. The setpoint is X*oil_flow_rate. Where X is whatever ratio you have to add the additive at. A feedback would be actual additive flow rate. Is the additive pump a positive displacement pump?
Been working with PLCs for a couple of decades, but almost 100% DirectLogic. Have a customer who wanted me to make a couple of simple changes to a...
1,122
New to the EcoStruxure programming software (I'm an AutomationDirect guy) and I've been banging my head against the wall trying to figure out how...
1,022
I haven't had to tune a PID loop in a very long time. It's actually a PI loop for a pulse width modulation s.v. What was the name of that tuning...
4,114
So I have a PID loop on an 1756-L61 running V17 software just for background. Also the PID PV is a pressure transmitter and the CV is speed sent...
894
Hi All I'm using Cohen-Coon method to calculate initial PID parameters. So, I have Model Gain that has been calculated from live data. Could...
55
31,104