Old February 8th, 2019, 10:39 PM   #1
delforum
Member
United States

delforum is offline
 
Join Date: Jul 2014
Location: US
Posts: 7
Post RSLogix 1756-L71 Read Only Tamperproof Tags

Hello PLCTalk Experts,

I am looking for an elegant solution to allow viewing of the tags current real values in the database by an unauthorized user, but also prevents the other RSLogix user from ever changing the array of real numbers in that tag.
Do you have any suggestions on how to setup the ladder or AOI using source protection to lock the routine?
  Reply With Quote
Old February 9th, 2019, 12:52 AM   #2
James Mcquade
Member
United States

James Mcquade is offline
 
Join Date: Oct 2007
Location: Tennessee
Posts: 2,316
I can understand why you would want to keep maintenance from making program changes, but WHY would you want to keep another programmer from making changes?

my coworker trust each other and we make changes all the time.
we discuss the program changes the next morning.

please explain your application in more detail.

regards,
james
  Reply With Quote
Old February 9th, 2019, 08:48 AM   #3
collinsd70
Member
United Kingdom

collinsd70 is offline
 
Join Date: Feb 2014
Location: Swindon
Posts: 91
Quote:
Originally Posted by delforum View Post
Hello PLCTalk Experts,

I am looking for an elegant solution to allow viewing of the tags current real values in the database by an unauthorized user, but also prevents the other RSLogix user from ever changing the array of real numbers in that tag.
Do you have any suggestions on how to setup the ladder or AOI using source protection to lock the routine?
Why not just write a constant value to a tag? This stops any changing of values during runtime or choose the 'constant' propery in the Controller Tags?


Regards

Daniel
  Reply With Quote
Old February 10th, 2019, 10:01 AM   #4
delforum
Member
United States

delforum is offline
 
Join Date: Jul 2014
Location: US
Posts: 7
Safety of the equipment is the main concern. If those tags change the equipment could be damaged by higher than rated pressures. Adjustments need to be made but infrequently and only by trained service.

With the constant property marked, what steps would be needed to change the register value? Can it be changed while in remote run online?
  Reply With Quote
Old February 10th, 2019, 10:02 AM   #5
collinsd70
Member
United Kingdom

collinsd70 is offline
 
Join Date: Feb 2014
Location: Swindon
Posts: 91
Quote:
Originally Posted by delforum View Post
Safety of the equipment is the main concern. If those tags change the equipment could be damaged by higher than rated pressures. Adjustments need to be made but infrequently and only by trained service.

With the constant property marked, what steps would be needed to change the register value? Can it be changed while in remote run online?
I believe the constant tag value has to be amended offline and downloaded complete but im not 100% sure on this.


Regards

Daniel
  Reply With Quote
Old February 10th, 2019, 12:23 PM   #6
collinsd70
Member
United Kingdom

collinsd70 is offline
 
Join Date: Feb 2014
Location: Swindon
Posts: 91
Quote:
Originally Posted by delforum View Post
Safety of the equipment is the main concern. If those tags change the equipment could be damaged by higher than rated pressures. Adjustments need to be made but infrequently and only by trained service.

With the constant property marked, what steps would be needed to change the register value? Can it be changed while in remote run online?
Hi Delform.

I have checked this for you on Emulate 5000, so the constant is declared via a Constant 'checkbox' in the Controller Tags and the value can be freely ammended offline/ online using the monitor tags window.

If an attempt is made to write to a constant tag through a routine; a compiler error is generated, so basically the value can only be updated directly.


Regards

Daniel
  Reply With Quote
Old February 10th, 2019, 01:51 PM   #7
Phrog30
Member
United States

Phrog30 is offline
 
Join Date: Dec 2006
Location: Montgomery, Alabama
Posts: 467
If it's that important, hard code the values in a move instruction in a protected routine. Only give the source key to the ones that you want to change. Anyone can still view in the tag database.
  Reply With Quote
Old February 10th, 2019, 03:05 PM   #8
delforum
Member
United States

delforum is offline
 
Join Date: Jul 2014
Location: US
Posts: 7
Thank you Daniel, James and Phrog for your insights. The constant tag may work well if I can put it in a protected AOI local tag database. Then in authorized persons couldn't change that tag value. How would I get that value from an AOI tag into my main task's routine?

Putting move instructions in a source protected routine seems like the simplest solution. A person with the correct protection key could edit the rung online, while others could only view the values.
  Reply With Quote
Old February 10th, 2019, 03:11 PM   #9
dmroeder
Lifetime Supporting Member
United States

dmroeder is offline
 
dmroeder's Avatar
 
Join Date: Apr 2006
Location: Vancouver, WA
Posts: 2,123
I would go with source protection rather than AIO, If you put them into an AOI, you are going to have to download every time you want to make changes.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Logix 5000 install problem smiller LIVE PLC Questions And Answers 16 May 26th, 2015 10:47 PM
Controller/Program tags not visible in RSLogix 5000 Joshua37 LIVE PLC Questions And Answers 14 December 11th, 2014 04:28 AM
RSLogix 5000 Controller Tags andrewke1 LIVE PLC Questions And Answers 5 October 8th, 2007 11:14 AM
how to read direct link tags in VBA? briana banks LIVE PLC Questions And Answers 4 April 1st, 2006 12:47 PM
How to read tags from Simatic MP370? avnerharel LIVE PLC Questions And Answers 10 June 8th, 2005 04:29 AM


All times are GMT -5. The time now is 10:27 PM.


.