4 - 20 MA 4 wire to 2 Wire Conversion
cbe.krishna
Apr 2010
coimbatore
Dear all,
We using 2 wire 4-20 MA analog input module , (siemens ET2OOS Module)we have to connect these inputs channels to VFD and Field Analog sensors which is active device in a four wire connection.
We are in trouble to replace 2 wire module to 4 wire module so kindly anybody reply how to solve this case, any isolators are 4 wire to 2 wire converters is there, if possible Pls reply low cost converters make & mdl no.
Thanks & regards
kk
It's all abuot knowing electronics - passive and active analog output of devices...
If You are not familliar with this, then go to Weidmuller site and download catalog:
4.1 Electronics – Analogue Signal Conditioning.
You will find there many devices that gives you what you need, and schematics too.
Wire the analog output from the 4 wire device to the Siemens card as shown below:
The other 2 wires on the 4 wire device are for power.
Thank you for reply,
I think that The wiring drawing shows the 2 wire loop powerd connection, in my application the field devices have the external 24 dc power supply will be in the 4 wire connection type.( VFD speed feedback,Ultrasonic sensor & resolver , 2 wire for power & 2 wire for current )
regards
kk
What leads you to believe that DC power (to drive a 2 wire loop powered transmitter) is provided on M0+?
Yeah, it says, "2 wire measuring transducer is supplied by means of measuring circuits", but that's some German translation of who knows what?
In the end, 4-20 is two wires; a plus and a minus.
The manual is not infallible. Note that both terminals 5 and 6 are labeled M1+, there's no M1-. It's typical crappy technical writing.
I'm not a Siemens guy, I just have the manual to look at. It sure looks to me like ANY 4-20mA signal gets wired to M0+ and M0(-).
You've got the hardware in front of you. If you put a voltmeter on M+ is there 24Vdc, or some DC voltage capable of driving a transmitter present?
If you think M0+ and M0- has power to drive a loop powered transmitter, hook a loop powered transmitter up and see if it turns on. I don't think it will. I suspect that DC power supplied to N.C. might be used to power a loop.
I find it invaluable to draw the loop and follow the current around the circuit, drawing arrows on the diagram as I do so.
Two wire has power and signal on the same circuit. Four wire has separate circuits for power and for signal. Three wire has a separate circuit for power and for signal, but they share the connection to the minus side of the power supply, closing both loops with a single wire.
The input doesn't care - it just sees signal current in and out.
And here is a pretty picture to go along with the above.
Hey Hive Mind, I am in the process of installing a L330ER with some 5069-IF8 IO cards. Some of my existing sensors are 3-wire 4-20mA. How are you...
5,377
I am supplying a control system to Singapore. The range of AWG wire size for the main breaker is 3/0 to 500 mcm. How do I put this in European...
2,726
Does anyone have experience wiring this type of analog pressure transmitter up? It's 4 wires. 3 blacks and 1 green which I assume is earth...
264
Hi everyone, I need some help I new with omron plc. I using plc CP1L. When I do the program it's good and the plc is function as program. But when...
86
Hi there, Trying to get some ascii serial communications working via RS485 (COMMREQ functions). I have attached our wiring for the COM2...
973