DF1 full duplex protocol - AB PLC5 to Proface 2400
Jan 2003
I have a client who has replaced an obsolete HMI with a PROFACE 2400.
The original HMI was connected to the AB PLC5 using the DF1 full duplex protocol.
HOW CAN I USE DF1 POINT TO POINT (FULL DUPLEX) TO COMMUNICATE BETWEEN THE AB PLC5 AND THE PROFACE 2400?
DF1
You can only use DF1 protocol if the device is compatable.
You configure chanel (0)zero on the PLC-5 for point to point using the configuration screen. Actually an easy process, don't sweat it.
Ref. A-B Publication #1785-6.5.12
Page 11-6
Why must you use DF1 protocol?
Good luck
Roger
DF1
I can not locate A-B Publication #1785-6.5.12 on the "AB Manauls Online" web pages.
Any ideas where I can get this info?
Or would it be possible to email page 11-6?
The reason to use Df1 is that the replacement HMI is one of a bank of interchangable unit and all the other devices are using this protocol. All the othe other devices would have to be changed $$$$$$$$
Best regards,
Darren
DF1 Master Slave Success
It works
All the information provided was correct
"THE BUG BEAR WAS THAT BOTH THE PLC AND THE HMI MUST HAVE THE SAME NODE ADDRESS I.E. 1, WHEN OPERATING AS DF1 MASTER SLAVE"
Thank you very much for your help
beerchug
Best regards
Darren
I am working on setting up a Prosoft Datalogger model PLX51-DLplus-232. This unit will be collecting data from a SLC 5/05 on the DB9 port set to...
103
Hi, I appreciate any help to make connection between AB DF1 Micrologix 1200 and WinCC Adv project (PC station - not HMI) possible. For now I can...
604
Hello everyone. I'm new on this forum and this is my firs thread. I have problem with AB 1679-L31 tags. There are tags group (tepe INT[256]) in a...
1,100
I'm trying to convert an old panelview 600 application to the 800 and I'd like to keep the current serial comms configuration instead of adding...
597
Hi all, I am attempting to communicate between PC and AB compactlogix L32E Using Logix 5000. FTLinx is able to communicate via ethernet. FTLinx...
1,846