4-20mA TO propotional valve control
It looks like you have V1 and V2 defined in 2 places.
You have them defined in PLC_PRG as local variables
AND
You have them defined in the I/O table.
Because of this, when you are writing to V1 or V2 within you PLC_PRG, you are only setting the values of the local variable.
Try to comment out V1 and V2 definitions in PLC_PRG and see if that works.
Hi all, I'm connecting several 4-20mA sensors together in parallel (only one shown below) The enclosure is ABS plastic with metal backplate DAQ...
274
Problem: Our PLC can only output 4-20mA, but the actuators it needs to control, modulate based on a 0-135Ohm signal. Buying 4 or 8 individual...
275
What's your go to 4-20ma isolator. I've got some 4 wire 4-20ma from several flow meters and scales that I would like to isolate before it gets to...
1,693
Hi, I need to read three 4-20mA signals from a DCS(ABB) in a remote 6 channel analog input module with RS485 modbus port. When I connected...
486
Hello this is my first post. Looking forward to being more involved in this community to learn and hopefully help others. Any help or guidance...
790