i have an int that is a 1 second increment for something
when a change in the int happens regardless of up or down i want a move to take place
any ideas how to do this?
i wanna trigger the rising edge of a bit change to trigger a an osr to a move
any ideas?
I've never used the OSR instruction. I usually use the ONS. This triggers when the rung conditions before it are true. Check out the instruction help for the ONS, they should have examples.
If you are trying to detect a change in the Int, you probably need to create two "temporary" Int tags, one for the current value of the Int and one for the previous value of the Int. Then check if they are equal (EQU instruction). If not equal, then trigger your move.
Hope this helps.
any ideas?
No big deal. I do stuff like this ... a lot.
Type in the rung this way, use your own names for the integers and bits..
INT_CHANGING is your integer that changes each second
INT_LAST is the value of INT_CHANGING last PLC scan
BOOL_TRIGGER is the output of the OSR that you examine in the rest of your program
BOOL_STORAGE is the internal storage for the OSR
INT_STORAGE is where you move INT_CHANGING to when it changes
Sorry for old school, but I'm not near my programming machine so I can't type it in and do a screen capture.
Code:
NEQ INT_CHANGING INT_LAST OSR BOOL_TRIGGER BOOL_STORAGE
XIC BOOL_TRIGGER MOV INT_CHANGING INT_STORAGE
MOV INT_CHANGING INT_LAST
You can also do this with an ONS and all on one rung. If you just want to do the MOV and don't need the bit to trigger anything else in the program
Code:
BST NEQ INT_CHANGING INT_LAST ONS BOOL_STORAGE MOV INT_CHANGING  INT_STORAGE NXB MOV INT_CHANGING INT_LAST BND
I can't remember if the DTR instruction exists in Logix 5000, but if not, then follow the advice of A_G and use NEQ followed by MOV where the source B in both instructions is your "last scan copy" of the data you want to detect a change in. The DTR (Data Transition) instruction does the same thing, but packs the NEQ and MOV into the same instruction. It is the only instruction I know of that is destructive but also has a rung out condition so that it must precede other instructions on a rung. I recall the DTR instruction in the PLC-5 so it may or may not have been included with RSLogix 5k.
Hi i would like to ask! Im using Omron CP1E PLC May i know how to use one input to trigger two outputs alternatively? Meaning press X0 on, Y0...
420
Hi all, I use e won for my OPCUA to back up my PLC (B&R X20 system) data. Whenever e won does maintenance updates, I need to reboot the e won in...
489
Hello ladies and gents I’ve hit a road block on a project, it’s AB for preface this is a converting line including Winder tailsealer and...
822
Hi, I'm using CX Programmer and just seeing what the best way to trigger an output from the plc clock time would be. I need this to come on at 9am...
1,776
I am trying to have my Alarm Summary page open when an alarm goes active (I am using ALMD blocks) this is the expression I am trying to use...
1,265