Danfoss VLT FC 100 Torque limit
crawler009
Feb 2012
Planet Earth
239
Hello Guys,
i have a strange problem with some Danfoss VLT FC 100 Frequency inverters.
We have sometimes a little overload (we have to work on that), and the Motor reaches his torque load. The VLT 100 limits the output current (and frequency) and shows a warning (12 Torque limit). So far everything is normal.
Now the weird thing:
When the inverter shows warning 12, he doesnt accept any commands from the terminals, and continues operating at the last frecuency. I have the signals "start", "auto start", and the analog signal (0-10) for the speed.
An example: I give the start signals and 10V for 100% speed. The inverter goes to 97% and stays there, showing warning 12.
If i reduce the analog signal to 5V, the inverter stays at 97% with his warning. Now i reduce the load, so that the warning goes away, and then the speed goes down to 50%.
If the inverter is in warning state with 97% speed, i can even remove the "start" and "auto start" signal, and nothing happens. If a reduce the load, then he goes up to 100%, taking the alarm away and then shuts off.
Had anyone experience with this problem and a posible solution? Like my load may vary, i cannot assure that the inverter never goes into torque limit, but i want him still to listen to my commands.
Best regards,
crawler009
I would find that kind of behavior unacceptable from a safety standpoint. Any vfd that does not stop when the Run command is removed should be red-tagged and taken out of service immediately (assuming two wire maintained start/stop control).
Hi Crawler!
Are we talking FC101 or FC102?
What is the firmware of the drive?
It does not look like it, but do you have Terminal 27 connected? This terminal is default "Coast Inverse" and I would expect this one to work in all conditions.
I do agree that a drive should react on its input no matter what, but the coast function of a Danfoss drive will have higher priority than the Start/Stop.
Best regards,
Michal_dk
Hello Michal_dk,
the Terminal 27 "Coast Inverse" is working fine (if i open the door). But dont want to trigger that signal, just to slow down (a little bit) the motor, its not like it should be. Im using Rockwell inverters (in most mashines) and they are working fine, even during warning state.
Its a 102, i just cant get firmware version right now (cause they are at a clients place). But its a new inverter, orderd like 3 months ago.
Best regards,
crawler009
Hello all. I am hoping someone here has installed a Danfoss VLT Midi FC 280 and connected an encoder to it. I am just trying to make sure I select...
486
Having a small problem with a new danfoss micro VLT FC51 drive I was hoping someone on here could help with. my setup: my motor speed is...
1,449
Hello everyone, I am an engineering student who took on a project to design and build a control system for an industrial coffee roaster as my...
4,581
Hi all, Got a Danfoss FC102 VLT drive which reverts to Off mode whenever I cycle power to it. I'm controlling it over ethernet from a Control...
1,870
Hi all, I am having a problem with 3 VLT 2800 drivers. All are showing on occasion error 16. I know that this points to short circuit on the...
2,312