Factorytalk ME Error Msg: Trigger has been disabled...
aliceqrd
Oct 2018
Washington
Hello,
We are getting the error message on PV plus 7 saying: "{Tagxx} This trigger has been disabled as its data type is not supported by Bit or LSBit tr*" The display is small and doesn't show the rest of the message; I am not sure how to get the rest of the message.
In the PV program, the tag is associated with a MultiStateIndicator of 2 states. In the PLC code the tag is connected with bit address. When I tested the display with the controller online the indicator works fine.
Additionally, I saw some threads along the same (start of) error message; following that advice, I made sure the trigger type is value. However, the error msg still pops up. Though other multistateindicator on the same display/in the same program does not trigger this error.
Any advice on how to solve this bug would be greatly appreciated. Thanks in advance!
Other Context info:
-we are converting from panel builder 32 .pva/.pvb file to .mer file; we have ensured that the tags are correctly formatted
-using factorytalk ME release 10 downloaded to PV 7 plus
Hello,
Use Factory Talk Diagnostics Viewer. You'll find in Windows under All Programs> Rockwell software>Factory Talk Tools> Diagnostic Viewer.
Thanks for the advice. We end up solving the issue by deleting the problematic object and creating a new object with identical settings and connections which solve the problem...magical... I think is probably some conversion error residue.
I upgraded Factorytalk activation manager to version 5.01 from 5.00 and since then, Factorytalk Assetcentre stopped working! I receive the...
462
"Failed to Initialize the service {3F883B87-2208-11D4-B0E7-001083022E04}" Along with "Failed to load HMI Server Service" Hello, I am getting...
749
Hello all, I am trying to "Specify a FactoryTak directory" to another computer on the network. But my local admin username and password generates...
1,682
I have uploaded a file from a panelview and i get a message when trying to restore it: "This runtime application file was saved in a protected...
1,356
Hi All, I create a new project at Factorytalk Local station and a OPC DA server with localhost server. FTView Version :13.00.00 OPC Server...
4,173