Can't delete RSLOGIX and FACTORYTALK tags

Dear all:
In our plant I have an ALLEN BRADLEY PLC 1756-L73 for controlling the plant and an AADVANCE PLC for safeguarding system. For the HMI I have FACTORYTALK monitoring both. For AADVANCE the communication with FACTORYTALK is through an OPC server that uses MODBUS to communicate with the PLC. HMI tags are defined in FACTORYTALK corresponding to the tags in the AADVANCE PLC. Then these HMI tags in FACTORY are used for alarming and graphics connections etc. For the RSLOGIX the controller tags are referred to directly by FACTORYTALK.
Recently we decommissioned two pumps. I wanted to remove every thing related to them in the system. I removed all the logic , the graphics, the alarms , data log... etc that is related to them. When I wanted to remove the tags I couldn't remove some tags from RSLOGIX online. I got a message that these tags are being used. The same happened when I wanted to remove the HMI tags used by FACTORYTALK to connect to the AADVANCE PLC tags. I'm sure I have removed all the references to these tags.

As all the tags that I was denied to delete look to have something to do with alarming, could it be that the alarm server is still monitoring them?
How can I delete RSLOGIX tags from the alarm server?
WHat about factory talk HMI tags? I stopped the data logging and restarted it. I stopped alarming together then restarted it but the problem persisted.
Any suggestions?
  Reply With Quote
Old September 26th, 2017, 07:03 AM   #2
spaderkung
Member
Sweden

spaderkung is offline
 
Join Date: Aug 2007
Location: A flat type "4"
Posts: 342
Is there an option for the alarm server to Start on windows or Start on client connects? Then change and restart pc, then services are stopped. I have used this for other cases than yours though..
__________________
Jon Bolmstedt, Inspired Automatician.
  Reply With Quote
Old September 26th, 2017, 07:34 AM   #3
AFPC
Member
Syria

AFPC is offline
 
Join Date: Feb 2011
Location: Damascus
Posts: 7
Quote:
Originally Posted by spaderkung View Post
Is there an option for the alarm server to Start on windows or Start on client connects? Then change and restart pc, then services are stopped. I have used this for other cases than yours though..
Thank you for the response
The problem that by restarting the server machine, the operators will be blind for a while to the critical measurements from the AADVANCE. The safety standards of our company don't allow that even for a brief minute without shutting down the plant.
  Reply With Quote
Old September 26th, 2017, 08:28 AM   #4
Mispeld
Member
United States

Mispeld is offline
 
Mispeld's Avatar
 
Join Date: Feb 2017
Location: VA
Posts: 340
The option exists to delete the unused tag(s) in an up-to-date offline file and then download to the processor. This would require downtime on the machine, but would force the communication process (e.g., RS-Linx) to refresh its connection with the machine. Assuming the deleted tags are no longer referenced by server processes, all should be OK.
  Reply With Quote
Old September 26th, 2017, 11:09 AM   #5
AFPC
Member
Syria

AFPC is offline
 
Join Date: Feb 2011
Location: Damascus
Posts: 7
Quote:
Originally Posted by Mispeld View Post
The option exists to delete the unused tag(s) in an up-to-date offline file and then download to the processor. This would require downtime on the machine, but would force the communication process (e.g., RS-Linx) to refresh its connection with the machine. Assuming the deleted tags are no longer referenced by server processes, all should be OK.
Thank you for the response. But this will need a plant shutdown.
  Reply With Quote
Old September 26th, 2017, 12:34 PM   #6
jstolaruk
Member
United States

jstolaruk is offline
 
Join Date: Dec 2004
Location: Detroit, SE Michigan
Posts: 3,240
Quote:
Originally Posted by AFPC View Post
Thank you for the response. But this will need a plant shutdown.
No harm in just allowing the unused tags to exist. Delete them before the next download.
__________________
"You can live to be a hundred if you give up all the things that make you want to live to be a hundred." Woody Allen
  Reply With Quote
Old September 27th, 2017, 01:24 AM   #7
AFPC
Member
Syria

AFPC is offline
 
Join Date: Feb 2011
Location: Damascus
Posts: 7
Quote:
Originally Posted by jstolaruk View Post
No harm in just allowing the unused tags to exist. Delete them before the next download.
Probably this is the only choice I have. Thank you
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
how to use rslogix 500 addressing with factorytalk view m.e. ? sameer.bhaskarla LIVE PLC Questions And Answers 4 March 28th, 2016 03:29 PM
RSLogix 5000 and FactoryTalk View Studio Question tranmeister LIVE PLC Questions And Answers 21 July 30th, 2015 03:33 PM
How do I move PLC tags directly into VBA variables inside FactoryTalk View 7.0? Gi1gamesh LIVE PLC Questions And Answers 0 June 19th, 2015 11:20 PM
Logix 5000 install problem smiller LIVE PLC Questions And Answers 16 May 26th, 2015 09:47 PM
UDT tags in FactoryTalk ME xzen LIVE PLC Questions And Answers 2 August 15th, 2013 02:44 PM


All times are GMT -5. The time now is 08:18 AM.


.