plc storereviewsdownloads
PLC training tools sale
Reply
Thread Tools Display Modes
Old December 5th, 2017, 02:05 AM   #1
Rob...
Supporting Member
United Kingdom
Rob... is offline
Angry TIA Portal V14 - Tag Comments
Ok, so I've recently been given a project to do in portal V.14 after a good few months using studio 5000.
I know there isn't a way to do this in V.13.1 that I was previously using but was hoping dearly that this would have been fixed in this update.
Is there any way to show tag comments above the tag when programming in LAD, like studio 5000 (and every other software package I've used do!).
I know Siemens are going down the symbolic tag route, but as everyone knows the more description you can add to your code, the easier it is for someone else/maintenance to deal with down the line.
Old December 5th, 2017, 03:55 AM   #2
VictorBit
Sweden
VictorBit is offline
VictorBit's Avatar
Hello Rob,
There is,
1.Options
2.Settings
3.PLC programming
4. Under general settings for PLC programming you have the possibility to change the View ( at the operand representation)
//Vic
Old December 5th, 2017, 03:57 AM   #3
VictorBit
Sweden
VictorBit's Avatar
Please see the following picture
Old December 5th, 2017, 05:14 AM   #4
Rob...
Supporting Member
United Kingdom
Rob... is offline
VictorBit
Taken a look at that, and it's not what I'm after unfortunately.
Thanks for the input.
Old December 5th, 2017, 07:07 AM   #5
mk42
United States
mk42 is offline
Rob,
I think it's actually the setting right after the ones he circled. Set "Location of tag information" to "At LAD/FB address".
However, this capability was only introduced in V14 SP1, so if you're at 14 with no SP then you'll need to upgrade. I've been waiting for this for years.
Old December 5th, 2017, 07:36 AM   #6
Rob...
Supporting Member
United Kingdom
Rob... is offline
Well, we get all the updates as an SI, so I'll dig that out. Update to SP1 and get back to you all.
Thanks!
Old December 5th, 2017, 01:08 PM   #7
kalabdel
Canada
kalabdel is offline
View menu will give you access to those options.
The "Tag Information" option above the one shown in the picture should have what you're looking for
Old December 6th, 2017, 06:47 AM   #8
JesperMP
Denmark
JesperMP is offline
JesperMP's Avatar
I always choose "below LAD/FBD network".
If you choose "at LAD/FBD network" then the networks bloom out and becomes unreadable just because of the size.
__________________
Jesper
3 strikes and you're out
Old December 6th, 2017, 07:16 AM   #9
mk42
United States
mk42 is offline
The downside of comments below is that you need to cross reference the tag above in the logic with the tag below with the comments. If there is a complex rung above it, the table can get rather beefy. It takes up less space overall, but it makes it harder to match a tag to its comments.
The reason this becomes important (in my experience) is that I work with a lot of Rockwell programmers who are used to the tag comment and tag name being always together in the code, and the tag comment ends up being pretty much required to understand what is going on. I see many situations where the wire number (VL1551) is the tag name, and the actual function is the description (Hot water valve open). I also see countless situations where they have an array of bits (in a DINT) with different comments for each of the bits to indicate its use, and they are pretty much meaningless without the comments.
There are other ways to solve these problems via Siemens best practices, but most of the systems I work on have dual spec Siemens & Rockwell, and the Siemens code spec was written by an AB trained guy who wanted it to match exactly.
Old December 6th, 2017, 07:36 AM   #10
JesperMP
Denmark
JesperMP is offline
JesperMP's Avatar
I guess that for comments "at LAD/FBD network" you need to selfimpose a limit to the length of the tag comments. I tend to be quite verbose, better too much than too little.
The tag symbols on the other hand must be reasonably meaningful. So much that they really help with the understanding of the code. I mean, why have symbols if they dont help; you could just as well remove the symbols altogether.
I name symbols after the connected item which follows functions and item naming, plus a small helpful description, i.e. for a sensor it could be "=W1-BG2_end_position".
To use wirenumbers sounds a really bad choice IMO.
__________________
Jesper
Old December 6th, 2017, 07:55 AM   #11
Rob...
Supporting Member
United Kingdom
Rob... is offline
We will generally use tags relating to the P&ID drawings.
So for instance AVxxZSO
(Automated Valve xx Open Limit)
Where the xx designation would be a number, an I would normally write a comment such as "Plant Inlet Valve Open Limit".
I have a excel sheet built up that auto generates tags, comments and lays them out ready for importing into Logix, AutoCAD. Saves a huge amount of time.
However just having a tag AVxxZSO won't mean much for maintenance or someone new reading the code without prior knowledge of the plant or looking all over the P&ID.
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
Siemens TIA Portal V13 Help Nan LIVE PLC Questions And Answers 7 May 18th, 2017 12:40 PM
Siemens TIA Portal V13 EZMarquee Help Nan LIVE PLC Questions And Answers 9 May 18th, 2017 12:38 PM
Siemens SIMATIC WinCC TIA Portal v14 - Is Indirect tagging Possible? DenZ_P LIVE PLC Questions And Answers 2 January 24th, 2017 05:51 AM
Upload and version problems with TIA Portal Wino LIVE PLC Questions And Answers 3 August 6th, 2015 11:43 AM
STL comments Tia Portal doyke14 LIVE PLC Questions And Answers 0 April 10th, 2013 03:40 AM
