tia portal v14 modbus

RY_Guthrie

Member
Join Date
Nov 2011
Location
Las vegas, NV
Posts
263
I am trying to commission a compressor that is using a s7-1200 to communicate rs485/modbus to a the compressor interface. My rs485 module is a cm-1241. I have no tx or rx lighs on the module, the program seems to be not connecting to the "slave" at the compressor. I have the mode set to 4 which I believe is rs485 on mb master fb, I have the baud, parity, stop bits set correctly I believe in my mb_comm_load i also think the port is correct. (see pics of both)I am wanting to use a modbus slave on my laptop to try and determine which end the problem is on. Can anyone first off see any obvious issues with the modbus setup form the pics? And what is a good modbus slave simulator to use? Thanks

modbus master.jpg modbus comm load.jpg
 
Modbus com load pin MB_DB should point to DBx.MB_DB parameter, now it only points to whole DB32-area.


I think that it should be %DB32.dbx24.0. (MB_MASTER_DB_1.MB_DB symbolically with your symbols.)
 

Similar Topics

Hi everyone. Please help me to upload program from S7-1200 with TIA v14. I created new project, go to Online tab, select Upload devices as new...
Replies
0
Views
1,084
I am beatin gmy head against the wall trying to get my modbus comms working. I have a s7-1200 running tia v14, a cm-1241 comm card. I have...
Replies
22
Views
7,403
Is it possible to install Siemens Tia Portal V14 on a machine that already has V16 installed? Or do I need to create a virtual machine to install...
Replies
17
Views
8,895
Is anyone know how to change the state of Button and multistate indicator(for Verify changing in color and text) in TIA portal HMI while doing...
Replies
1
Views
1,323
Hi all, I'm working on migrating some old Sinamics S120 drive units currently integrated in Step 7 5.6/WinCC Flexible 2008 RT to TIA Portal V14...
Replies
7
Views
3,394
Back
Top Bottom