Question regarding Ethernet/IP vs Analog I/O

This may be a simple question.
I understand the concept and application of analog modules (i.e. Compactlogix) for transducers, and outputs for VFD speed reference and such but my question is regarding the use of Ethernet/IP for the analog. For example we have a couple Ethernet based SICK encoders that do not report to a HSC module--there isn't one on the rack and Drives are speed referenced thru Ethernet as well....does this indicate the analog and signals are traveling thru the Ethernet and these modules are not necessary as the code is being handled in the controller without the dedicated module interface of a HSC or Analog input/output modules?
  Reply With Quote
Old March 6th, 2018, 09:40 AM   #2
jraef
Member
United States

jraef is online now
 
jraef's Avatar
 
Join Date: May 2006
Location: Northern California
Posts: 1,527
Yes and no. The actual analog SIGNALS are not being transmitted in the Ethernet media. The analog values are being converted to digital values, and those digital values are what is transmitted within a packet of data from device to device. Since whatever needs that information was going to convert analog to digital internally anyway, it ends up the same and in fact can acutually avoid errors in transmission of the analog values over long distances. In your example if the SICK encoder has an Ethernet I/P output port, that means is had the transducer (HSC) built-in that is doing the converting to a digital value right at the encoder and making it available to the Ethernet I/P network.
  Reply With Quote
Old March 6th, 2018, 09:57 AM   #3
toddp65
Member
United States

toddp65 is offline
 
Join Date: Aug 2014
Location: Florence, Ky
Posts: 26
Ok--so there's no actual analog travelling thru the Ethernet because, well, it's not capable of doing so, therefore the PLC is receiving digital data. So am I correct in assuming that control of a VFD, i.e. a Powerflex 525, the speed reference can be transmitted without an analog ouputt card and an analog output from the drive (amperage) does not need an analog input card-- so basically a controller without those modules is capable of performing these tasks?

thanks
  Reply With Quote
Old March 6th, 2018, 10:14 AM   #4
cardosocea
Member
United Kingdom

cardosocea is offline
 
Join Date: Nov 2016
Location: Fields of corn
Posts: 974
Quote:
Originally Posted by toddp65 View Post
Ok--so there's no actual analog travelling thru the Ethernet because, well, it's not capable of doing so, therefore the PLC is receiving digital data. So am I correct in assuming that control of a VFD, i.e. a Powerflex 525, the speed reference can be transmitted without an analog ouputt card and an analog output from the drive (amperage) does not need an analog input card-- so basically a controller without those modules is capable of performing these tasks?

thanks
Yes. Generally you can control every parameter of a drive... so not only the speed reference but the mode (speed versus torque control) and torque, current limits, etc...

You usually can also retrieve a lot of information from the drive such as faults and fault codes that can make it simpler for maintenacne to troubleshoot the system.
  Reply With Quote
Old March 6th, 2018, 10:22 AM   #5
toddp65
Member
United States

toddp65 is offline
 
Join Date: Aug 2014
Location: Florence, Ky
Posts: 26
Thanks--I was aware of that as I've added a 525 to a project before--I was just hazy about the interaction between an ethenet/ip device such as a drive or encoder or anything else analog (I've seen summing boards for scales) and the need or lack of a need for dedciated analog cards.


Thanks
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
directsoft 5 - how do I address analog I/O?? gr8benwa LIVE PLC Questions And Answers 5 January 2nd, 2017 02:08 PM
Ethernet/IP (I/O) across a gateway/router jdbrandt LIVE PLC Questions And Answers 3 September 13th, 2016 07:38 AM
Io neilot LIVE PLC Questions And Answers 6 June 30th, 2014 05:22 PM
Question on Analog Modules and SCP Instr. JoseM LIVE PLC Questions And Answers 2 April 4th, 2014 10:42 AM
SLC 5/05 with remote I/O & analog sparky mark 9876 LIVE PLC Questions And Answers 5 December 6th, 2008 04:44 PM


All times are GMT -5. The time now is 09:11 AM.


.