Old October 1st, 2003, 03:12 PM   #1
bmcombs
Member
United States

bmcombs is offline
 
Join Date: Jun 2003
Posts: 1
Power Flex 70 Drives on Device Net

I am currently working on a project using the Allen-Bradley Power Flex 70 drives and configuring them on Device Net. Also we are using PLC 5/40 E. When you configure a drive on D-Net, D-Net writes 2 words of memory per drive to the scanner module. In our ladder logic, we have to use BTR & BTW logic to configure these words. The max length of words in the BTR & BTW is 64. Well in our job, we are looking at configuring 42 drives! This means a total of 84 words of memory. How do I configure this many words of memory in my PLC. Can I use two sets of BTR & BTW to write the 84 words to the scanner module?
  Reply With Quote
Old October 1st, 2003, 11:02 PM   #2
Eddie Willers
Member
United States

Eddie Willers is offline
 
Eddie Willers's Avatar
 
Join Date: May 2002
Location: Grand Central Station
Posts: 615
Yup.

The 1771-SDN can actually accomodate several BTR/BTW sets to access a total of 357 words of DeviceNet Input and Output data.

If the PLC-5 is sending several block transfers to the same slot, the module can only tell them apart by size.

62 Words - BT #1
61 Words - BT #2
60 Words - BT #3
59 Words - BT #4
58 Words - BT #5
57 Words - BT #6

That's 357 words of Input, and 357 words of Output. That big old piecewise data table can be shared by both channels of the 1771-SDN.

Making a scanlist for both channels is kind of a clunky process; read the RSNetworx notes on that carefully.

The Installation Instructions for the 1771-SDN are the best reading on the matter. They're on www.ab.com/manuals
  Reply With Quote
Old October 2nd, 2003, 01:16 PM   #3
Berni
Member
Canada

Berni is offline
 
Berni's Avatar
 
Join Date: Aug 2003
Posts: 14
btr

Hi, yes you've gonna make two btr ab btw. First one in word #62 in the scanner and the second in word #61.
  Reply With Quote
Old October 2nd, 2003, 07:02 PM   #4
dash
Lifetime Supporting Member
United States

dash is offline
 
dash's Avatar
 
Join Date: Jun 2003
Location: Birmingham, AL
Posts: 589
Let me jump in here an warn you about a MAJOR problem with RSLogix 5 and the DeviceNet scanner.

DO NOT configure the 1771-SDN in the configuration wizard!! This will cause problems with the multiple BTR/BTWs' that you must perform to the module to get access to the total available 357 words that Eddie mentions. I worked with someone who did this in order to get access to the devicenet status data and it caused an automated crane to drop drop a charge bucket for an automated cupola charging system. Of course once the cupola is running you don't want to stop it so you can imagine how tense things (& the mechanics got the crane back in working order) were while he reloaded the old program. It took me a day to figure out that the chassis configuration was causing the issue. Of course Rockwell just says that they never use the configuration wizard anyway.

Just be careful. I can create an example file that will show the problem and it is visible in the offline file.

Darren

Last edited by dash; October 2nd, 2003 at 07:05 PM.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Device Net Faults LIVE PLC Questions And Answers 10 December 8th, 2016 11:15 PM
To Latch Or Not To Latch BOWRIDER LIVE PLC Questions And Answers 43 October 21st, 2015 04:19 AM
Analogue Inputs - Sink, Source, Help! Yabadabadoo LIVE PLC Questions And Answers 14 January 26th, 2005 12:48 PM
Device net and Allen-Bradley PLC question Ken Moore LIVE PLC Questions And Answers 9 November 18th, 2004 09:06 PM
History, Advantages & Disadvantages of DeviceNet CROSBY MENSAH LIVE PLC Questions And Answers 8 April 2nd, 2004 01:19 AM


All times are GMT -5. The time now is 12:59 PM.


.