Power Flex 70 Drives on Device Net
bmcombs
Jun 2003
I am currently working on a project using the Allen-Bradley Power Flex 70 drives and configuring them on Device Net. Also we are using PLC 5/40 E. When you configure a drive on D-Net, D-Net writes 2 words of memory per drive to the scanner module. In our ladder logic, we have to use BTR & BTW logic to configure these words. The max length of words in the BTR & BTW is 64. Well in our job, we are looking at configuring 42 drives! This means a total of 84 words of memory. How do I configure this many words of memory in my PLC. Can I use two sets of BTR & BTW to write the 84 words to the scanner module?
Yup.
The 1771-SDN can actually accomodate several BTR/BTW sets to access a total of 357 words of DeviceNet Input and Output data.
If the PLC-5 is sending several block transfers to the same slot, the module can only tell them apart by size.
62 Words - BT #1
61 Words - BT #2
60 Words - BT #3
59 Words - BT #4
58 Words - BT #5
57 Words - BT #6
That's 357 words of Input, and 357 words of Output. That big old piecewise data table can be shared by both channels of the 1771-SDN.
Making a scanlist for both channels is kind of a clunky process; read the RSNetworx notes on that carefully.
The Installation Instructions for the 1771-SDN are the best reading on the matter. They're on www.ab.com/manuals
btr
Hi, yes you've gonna make two btr ab btw. First one in word #62 in the scanner and the second in word #61.
Let me jump in here an warn you about a MAJOR problem with RSLogix 5 and the DeviceNet scanner.
DO NOT configure the 1771-SDN in the configuration wizard!! This will cause problems with the multiple BTR/BTWs' that you must perform to the module to get access to the total available 357 words that Eddie mentions. I worked with someone who did this in order to get access to the devicenet status data and it caused an automated crane to drop drop a charge bucket for an automated cupola charging system. Of course once the cupola is running you don't want to stop it so you can imagine how tense things (& the mechanics got the crane back in working order) were while he reloaded the old program. It took me a day to figure out that the chassis configuration was causing the issue. Of course Rockwell just says that they never use the configuration wizard anyway.
Just be careful. I can create an example file that will show the problem and it is visible in the offline file.
Darren
Hi All, While Replacing a VFD in breakdown condition which is the right and easy way to replace the drive quickly. We are working with Plant PAX...
1,518
How many power flex 40 drives can you run off one 1756/ENBT card without any significant performance hits? I've searched this site as well as...
3,206
Can I extract parameters froem my power flrx drive with RS5000 or do I need to purchase separate software from Rockwell ? Thanks
2,527
I was wondering if anyone knows a good link/ resource that explains how to program a micrologix 1400 to control a Power Flex 4 drive via RJ45...
3,397
We have several PowerFlex 4 drives around the plant.We had a planned outage that the power company was going switch over to another feed , after...
8,227