Had an interesting morning troubleshooting our scenery elevator today. It's been down for a few days, and I was asked to take a look.
Two days ago, we had a "partial" power failure. Our lovely city-owned electric utility lost a phase out of the substation for the south side of town. Since then, the elevator hasn't worked. Every time someone tried to operate the lift, its 120vac control power circuit breaker would trip.
Turns out the elevator derives its 120vac control voltage from a 480v-120v transformer. I'm guessing the transformer is tied to one of the phases that stayed on, and the one that died (not sure which phase we lost). The transformer was putting out something much less than 120v, but apparently enough to keep the switch-mode power supply happy enough to power the control PLC and thus everything 24vdc.
The main contactor is a 100A unit, with a 120vac coil; it switches power to the VFD, based on E-stop condition, etc... Near as I can figure, the control voltage was high enough to power the SMPS, but low enough to not pull in the contactor fully. The coil melted and eventually burned off enough enamel to cause it to become a dead short, thus tripping the control voltage circuit breaker on the transformer secondary. I never knew a coil could extrude so much molten, stinky plastic! Props to Allen Bradley for selling the coil as a separate part, even if it's too expensive (70% of the cost of a new contactor).
A new main contactor coil is arriving tomorrow, and a phase-loss monitor relay is showing up early next week. I plan on wiring that to switch 120v control voltage off if we have another phase-loss event with the utility. If the contactor is the only thing damaged, our elevator will hopefully work tomorrow.
It was an interesting morning to say the least. Time will tell if there's anything else the power failure cooked.
I have to remember to send the city electrical utility a thank you card once this is all done I'd have rather they kept everything off until their fault was fixed, instead of giving us partial power and damaging our gear. I haven't worked here too long, but this dropping-a-phase thing is apparently not uncommon.
-rpoet
Two days ago, we had a "partial" power failure. Our lovely city-owned electric utility lost a phase out of the substation for the south side of town. Since then, the elevator hasn't worked. Every time someone tried to operate the lift, its 120vac control power circuit breaker would trip.
Turns out the elevator derives its 120vac control voltage from a 480v-120v transformer. I'm guessing the transformer is tied to one of the phases that stayed on, and the one that died (not sure which phase we lost). The transformer was putting out something much less than 120v, but apparently enough to keep the switch-mode power supply happy enough to power the control PLC and thus everything 24vdc.
The main contactor is a 100A unit, with a 120vac coil; it switches power to the VFD, based on E-stop condition, etc... Near as I can figure, the control voltage was high enough to power the SMPS, but low enough to not pull in the contactor fully. The coil melted and eventually burned off enough enamel to cause it to become a dead short, thus tripping the control voltage circuit breaker on the transformer secondary. I never knew a coil could extrude so much molten, stinky plastic! Props to Allen Bradley for selling the coil as a separate part, even if it's too expensive (70% of the cost of a new contactor).
A new main contactor coil is arriving tomorrow, and a phase-loss monitor relay is showing up early next week. I plan on wiring that to switch 120v control voltage off if we have another phase-loss event with the utility. If the contactor is the only thing damaged, our elevator will hopefully work tomorrow.
It was an interesting morning to say the least. Time will tell if there's anything else the power failure cooked.
I have to remember to send the city electrical utility a thank you card once this is all done I'd have rather they kept everything off until their fault was fixed, instead of giving us partial power and damaging our gear. I haven't worked here too long, but this dropping-a-phase thing is apparently not uncommon.