Friday, 01/03/2014, at the end of the work shift, I was made aware that an Allen Bradley Ultra 3000 Digital Servo Drive faults occasionally with an E05 (Motor Over temperature) fault. I do not work in the area and was unaware of this problem. Our boss wants a solution. I talked briefly with the guy who runs the sealing equipment in that area and he told me the drive gets this fault a couple of times a day and he cycles power on the Ultra 3000 to clear the E05 fault and then the equipment will run again.

My boss said he notices it faults everyday about a half an hour after production is finished, equipment is idle. His office is only about 25 feet away from the equipment so when the Ultra 3000 faults an Alarm horn sounds (drives him crazy) he has to come out of his office onto the plant floor and silence the Alarm horn.

The operator of the equipment, in that area, said he also leaves the door of the Ultra 3000 Digital Servo Drive cabinet open to cool the drive control. But as I sit here at home (Saturday) thinking and writing about scenario I am realizing the OT Fault is on the Servo Motor.

These Ultra 3000 Digital Servo Drives are brand new to me no experience / training. I do not know at this moment what type/brand the Servo Drive Motor is - but do the Motors actually have a thermal switch/sensor on them? Im also thinking I should feel the Drive Motor to see if I actually feel any excessive heat.

The Ultra 3000 drives are on Device Net and we use A/B RS_Logix5000. On Friday, using Device Net, I quickly looked at the many parameters but do not know what they all are or if I can adjust any to get rid of fault - if Motor is not actually overheating.

If anyone can give me advice I would appreciate it. I would like to have some sort of a plan so when I go to work on Monday I can try and solve this problem. Thanks in advance.
  Reply With Quote
Old January 4th, 2014, 06:42 PM   #2
TWControls
Lifetime Supporting Member
United States

TWControls is offline
 
TWControls's Avatar
 
Join Date: Oct 2005
Location: Roanoke, VA
Posts: 2,081
Since it seems to happen at idle it could simply be a matter of poor tuning but...

When the alarm goes off has anyone felt the motor to see if it is actually hot?
  Reply With Quote
Old January 4th, 2014, 07:22 PM   #3
factoryrat
Member
United States

factoryrat is offline
 
Join Date: Feb 2010
Location: Michigan
Posts: 30
Quote:
Originally Posted by TWControls View Post
Since it seems to happen at idle it could simply be a matter of poor tuning but...

When the alarm goes off has anyone felt the motor to see if it is actually hot?
I am sure no one has felt motor. Like I mentioned the operator told me he opened the cabinet that houses the Ultra3000 Drive thinking that it would cool the Servo Drive. And it did not dawn on me until I started to write post that the Drive was not overheating it was the Motor.

If I can get over to that area of plant I will definitely feel Motor or have someone else do it.

What do you mean by tuning? I hope that is not a dumb question but I do not know. This equipment was installed and turned over to us to operate and maintain with absolutely no training and minimal documentation.

Last edited by factoryrat; January 4th, 2014 at 07:32 PM.
  Reply With Quote
Old January 4th, 2014, 07:34 PM   #4
TWControls
Lifetime Supporting Member
United States

TWControls is offline
 
TWControls's Avatar
 
Join Date: Oct 2005
Location: Roanoke, VA
Posts: 2,081
This is more of a Peter Nachtwey question, but pretty much most servo motors are always on or enabled, even when at rest. In theory they have 100% holding torque at zero speed. If tuning variables are not set right, it can try to "hold" too hard are rest and build heat.
  Reply With Quote
Old January 4th, 2014, 07:43 PM   #5
factoryrat
Member
United States

factoryrat is offline
 
Join Date: Feb 2010
Location: Michigan
Posts: 30
Quote:
Originally Posted by TWControls View Post
This is more of a Peter Nachtwey question, but pretty much most servo motors are always on or enabled, even when at rest. In theory they have 100% holding torque at zero speed. If tuning variables are not set right, it can try to "hold" too hard are rest and build heat.
Thanks. Every little bit of info helps.

Do you know if there is a manual or document that would walk a novice through this tuning procedure?
  Reply With Quote
Old January 4th, 2014, 07:56 PM   #6
Rob A
Member
United States

Rob A is offline
 
Rob A's Avatar
 
Join Date: Apr 2007
Location: Washington
Posts: 35
If this just started happening it could be something simple like loose pin connections in the encoder cable at the motor end. Power it down and try unplugging the cable and reconnecting the cable at the motor end.
It think there were some connection issues on the older style AB cables.
  Reply With Quote
Old January 4th, 2014, 08:15 PM   #7
factoryrat
Member
United States

factoryrat is offline
 
Join Date: Feb 2010
Location: Michigan
Posts: 30
Quote:
Originally Posted by Rob A View Post
If this just started happening it could be something simple like loose pin connections in the encoder cable at the motor end. Power it down and try unplugging the cable and reconnecting the cable at the motor end.
It think there were some connection issues on the older style AB cables.
I will get more history of problem on Monday. I wish I knew more now.

This Line was installed about one and a half years ago.

I think this problem has been going on for quite a while. It is a nuisance but can be reset quickly and has therefore been tolerated. There were a lot of other (more pressing) issues with this new automation that had to be troubleshot and fixed first.

I will take your advice and check connectors, cables, pin connectors. I will look for any kind of damage in work cell. Maybe something got damaged or connector is loose.
  Reply With Quote
Old January 4th, 2014, 08:15 PM   #8
TWControls
Lifetime Supporting Member
United States

TWControls is offline
 
TWControls's Avatar
 
Join Date: Oct 2005
Location: Roanoke, VA
Posts: 2,081
Quote:
Originally Posted by factoryrat View Post
Do you know if there is a manual or document that would walk a novice through this tuning procedure?
Not really. You'll be best to get someone who has some experience with it to help you if it is your first time.

First as Rob said, if it just started doing it or has began doing it more frequently, then first you should check the mechanical and electrical integrity of the system. System rarely just go out of tune.
  Reply With Quote
Old January 4th, 2014, 09:32 PM   #9
factoryrat
Member
United States

factoryrat is offline
 
Join Date: Feb 2010
Location: Michigan
Posts: 30
Quote:
Originally Posted by TWControls View Post
System rarely just go out of tune.
Thanks - I will keep this in mind.
  Reply With Quote
Old January 4th, 2014, 09:44 PM   #10
Gerry
Member
New Zealand

Gerry is offline
 
Join Date: Jun 2002
Location: Auckland
Posts: 1,142
Since it happens after production -- maybe the servo is driven to a
"park" position that it can't actually reach, either due to obstruction or some mechanical changes that have affected position calibration. This would have the drive applying increasing torque to try and reach the commanded position, but not getting any closer. Eventually, the motor thermostat trips.
  Reply With Quote
Old January 4th, 2014, 10:46 PM   #11
Rob A
Member
United States

Rob A is offline
 
Rob A's Avatar
 
Join Date: Apr 2007
Location: Washington
Posts: 35
Quote:
These Ultra 3000 Digital Servo Drives are brand new to me no experience / training. I do not know at this moment what type/brand the Servo Drive Motor is - but do the Motors actually have a thermal switch/sensor on them? Im also thinking I should feel the Drive Motor to see if I actually feel any excessive heat.

The Ultra 3000 drives are on Device Net and we use A/B RS_Logix5000. On Friday, using Device Net, I quickly looked at the many parameters but do not know what they all are or if I can adjust any to get rid of fault - if Motor is not actually overheating.
I know the Allen Bradley motors have thermal switches in them and the motors can run very hot (hot to the touch) without tripping the thermal switch. We run an MPL-B460 motor in a hoisting application and under normal operation you cannot keep your hand on the motor.
If the Ultra 3000 communicates over DeviceNet then it is an indexing drive. So move instructions(indexes) are programmed in the Ultra 3000. If you have the serial com cable and Ultraware software for the drive you can get online with it and look at the fault log. It might have some more information to help with troubleshooting.
  Reply With Quote
Old January 5th, 2014, 08:28 AM   #12
robertmee
Member
United States

robertmee is offline
 
robertmee's Avatar
 
Join Date: Feb 2008
Location: NC
Posts: 1,428
Quote:
Originally Posted by Gerry View Post
Since it happens after production -- maybe the servo is driven to a
"park" position that it can't actually reach, either due to obstruction or some mechanical changes that have affected position calibration. This would have the drive applying increasing torque to try and reach the commanded position, but not getting any closer. Eventually, the motor thermostat trips.
Unless it was programmed poorly, should get a position error fault LONG before heating up and overtripping due to trying to drive to position. I'm in the camp that if it has started happening it's a cabling issue...If it's happened since inception, it's a tuning issue. Also, without knowing the mechanics of this system, if the system is parked such that there are forces on the system acting against zero position (think trying to hold a flapper valve open against gravity), then the motor could certainly heat up trying to hold position.
  Reply With Quote
Old January 5th, 2014, 10:03 AM   #13
factoryrat
Member
United States

factoryrat is offline
 
Join Date: Feb 2010
Location: Michigan
Posts: 30
Quote:
Originally Posted by Rob A View Post
I know the Allen Bradley motors have thermal switches in them and the motors can run very hot (hot to the touch) without tripping the thermal switch. We run an MPL-B460 motor in a hoisting application and under normal operation you cannot keep your hand on the motor.
If the Ultra 3000 communicates over DeviceNet then it is an indexing drive. So move instructions(indexes) are programmed in the Ultra 3000. If you have the serial com cable and Ultraware software for the drive you can get online with it and look at the fault log. It might have some more information to help with troubleshooting.
Good information. I did not mention before but we have 7 more identical sealer applications in this area. So I will do the feel test on the other motors and compare temperatures with the faulty one. Hope I don't get a burned hand.

I would like to introduce another concern: As I was leaving work on Friday our Control Engr. was going to have a second shift Electrician swap faulting Ultra3000 Servo Drive with one of the others that does not get "Over Temperature" fault. We have two identical lines (North and South) so the swapped Ultra3000 Drives have the same Device Net Node Address. The reasoning was will problem follow Ultra3000 Drive or will the same motor fault with different Drive.

I'll find out Monday morning. But will this create any new problems? Do you guys think this will work or will it cause new problems. You can see we know nothing about these drives. We will learn - hopefully it will not be too painful an experience.
  Reply With Quote
Old January 5th, 2014, 12:20 PM   #14
kolyur
Lifetime Supporting Member + Moderator
United States

kolyur is offline
 
kolyur's Avatar
 
Join Date: Oct 2004
Location: Wooster, Ohio
Posts: 1,389
This is not a diagnosis but just my 2 cents:
We've used the Ultra 3000 drives extensively over the past 10 years or so. We've dealt with a handful of E05 errors during that time and I don't believe that any of them were actually due to the motor overheating. In all cases it was either a motor failure (bad overtemperature switch?) or a failed cable.
__________________
John
  Reply With Quote
Old January 5th, 2014, 12:45 PM   #15
factoryrat
Member
United States

factoryrat is offline
 
Join Date: Feb 2010
Location: Michigan
Posts: 30
Quote:
Originally Posted by kolyur View Post
This is not a diagnosis but just my 2 cents:
We've used the Ultra 3000 drives extensively over the past 10 years or so. We've dealt with a handful of E05 errors during that time and I don't believe that any of them were actually due to the motor overheating. In all cases it was either a motor failure (bad overtemperature switch?) or a failed cable.
Thanks John I will keep this in mind. I value this info and all the other information everyone has contributed. I am learning quite a bit.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
AB 1397 DC Drive - Fault Codes louielew LIVE PLC Questions And Answers 1 April 25th, 2012 10:55 AM
Roll Grinding CNC Machine Problem BIJOY LIVE PLC Questions And Answers 1 May 23rd, 2010 03:28 PM
Abb Ac Drive rajendrad LIVE PLC Questions And Answers 13 November 5th, 2006 10:18 AM
Heller milling machine controls and drive naveen LIVE PLC Questions And Answers 8 August 22nd, 2006 08:40 AM
Servo Positioning - AB - HSCE / NO4V Ramil LIVE PLC Questions And Answers 2 June 18th, 2003 07:27 AM


All times are GMT -5. The time now is 05:12 AM.


.