Hi all,
I have Modicon M241 PLC connected on Ethernet to a Magelis HMIS5T. Programming environment is SoMachine v4.1
I have managed to program the PLC, also prepared the HMI configuration, downloaded it, but the HMI doesn't communicate with the PLC. I get a "Failed to open connection to PLC. (PLC_SzennyKecsed). PLC_SzennyKecsed is the set nodename of the PLC. Interesting thing tough is that while simulating the HMI on the PC, communication is OK. The simulation can read/write the tags from the PLC. Programming PC runs Windows7 Ultimate 64bit.
Some things I should double check? Any suggestions?
Thanks,
Boti
Old January 29th, 2015, 01:13 PM   #2
jboti
Romania
jboti is offline
Problem solved. The PLC's IP address must be the same as the HMI's gateway.
Thought it might help someone.
Boti
Old January 29th, 2015, 03:03 PM   #3
CapinWinky
United States
CapinWinky is offline
CapinWinky's Avatar
You should leave the gateway as 0.0.0.0 unless your PLC is on a different subnet. By putting a gateway in place, you are telling the HMI to try to reach the PLC by routing through the gateway IP address (which is why it only works when PLC = gateway).
__________________
Cycling power is a sign of weakness.
Old January 30th, 2015, 12:35 AM   #4
jboti
Romania
jboti is offline
Hi CapinWinky,
Makes sense. Still, if the gateway was 0.0.0.0 the HMI failed to open communication.
Old October 1st, 2016, 08:20 AM   #5
ljoh
Denmark
ljoh is offline
Hello.
Old post, but I have exactly the same problem. I Download the program via ethernet and the program uploads. But I get the same connection error.
If I try to "download all" in SoMachine I can't get the HMI to download. Is it a problem with the device address of the PLC? I have tried to use gateway 0.0.0.0, PLC ip, routher ip.
Does anyone have a tip?
Old October 12th, 2016, 11:07 AM   #6
Engineer_MG
United States
Engineer_MG is offline
Engineer_MG's Avatar
1. Make sure that the Nodename of the PLC is the same on the HMI side under IO Manager ( Looks like you have)
2. Detach all the programming cables from the PLC/HMI as sometimes the active path maybe linking via the PC instead of the PLC ethernet/serial.
Hope this helps.
Thanks.
__________________
Ms. Engineer_MG
Senior Application Design Engineer
Schneider Electric , USA
Old October 12th, 2016, 05:13 PM   #7
ljoh
Denmark
ljoh is offline
Thanks for the tip :-)
I have a question. In vijeo designer under IO Manager/SoMachineNetwork there are two devices added: MyController and MyHMI. Does the nodename need to be the controller name in both?
I will try to detach the programming cables.
Old October 13th, 2016, 10:57 AM   #8
Engineer_MG
United States
The SOM_HMI part in Vijeo can have a generic name or it could take the active path name if you built the target in Vijeo Designer. It's there for activating a block driver that manages communication ( I don't know the in-depth reason - it's a secret in our RND dept. :-D )and doesn't need to have the exact PLC nodename.
The SOM_PLC part in Vijeo must have the exact nodename of the PLC. Make sure that the PLC has the active path set in the SoMachine side.
Hope this helps.
__________________
Ms. Engineer_MG
Old July 30th, 2017, 03:17 PM   #9
mazein
Canada
mazein is offline
This is related to this post. I was trying to connect a physical HMI (Magelis) to a SoMachine simulator running on a PC. In addition to making sure that the correct nodename for the SoMachine simulator is referenced in the Vijeo Designer, you also have to configure make configuration addition/changes to the Gateway Management Console located in the system tray in your Windows OS (Windows 7).
Below are the instruction for the configuration change in Gateway Management Console (GMC):
1. Open GMC by right-clicking on the Gateway-Tray-Applicaiton located in the System Tray, then selecting GMC
2.Once GMC window is open, select the Static Remote Connections tab
3.Type in the HMI address in "Remote IP address" field, then click on the button "Add connection"
4.Click OK to save the changes. This may have to be done each time you restart Windows, or SoMachine v4.1/4.2.
Hope this is useful to current, and/or future questions on this matter.
Regards,
Moukhtar Zein, CET
Automation Technologist
Old March 7th, 2018, 03:57 AM   #10
artyzver
Russian Federation
artyzver is offline
Boti
I have the same problem now, and HMI's gateway resets to 127.0.0.1 whenever i validate the hmi project. How do i change the gateway?
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
Connection problem Panelview Plus 600 Tarlo LIVE PLC Questions And Answers 2 December 6th, 2012 03:03 PM
Problem with S-7 connection (Two S-300) AsbianKS LIVE PLC Questions And Answers 11 November 24th, 2012 05:28 PM
problem of connection between a TSX Micro and Vijeo Citect v7.20 abdobouka LIVE PLC Questions And Answers 1 December 28th, 2011 03:24 AM
S5 Connection Problem pete66 LIVE PLC Questions And Answers 24 February 27th, 2008 03:00 AM
micrologix 1200 connection problem mehmetyil_99 LIVE PLC Questions And Answers 7 May 1st, 2007 03:41 AM