+ - 10 Volt Analog
The Plc Kid
Feb 2009
Macon, Georgia
3,233
How does the _+ 10 volt analog signals work? I have used 0-10 many times but i am trying to solve some problems on a hydraulic controller that outputs -10 to +10 it seems?
How do the end devices determine if the 10 volts is + or -?
In this case it a hydraulic servo valve. I assume i will need a source that will do -10 to +10 and all i have is a 0-10/ 4-20ma source. Can anyone recommend one?
The same way your multimeter does. There is always polarity with DC voltages. If you meter out a 24V power supply, and then swap your meter leads and meter is again, you would get +24V then -24V (or vice versa). It just depends which wire the +ve voltage is directed down.
Also, for a hydraulic valve, it is much simpler to have 0 volts correspond to the center position, than it would be to have 5 volts correspond to the center.
Plus, just think about what would happen to a servo valve or a motor drive using 0 to 10vdc for bidirectional operation, and a wire broke, or the controller faulted and the output went to zero...
With -10 to +10vdc, zero is stopped/centered, and the polarity corresponds to direction. bipolar voltage signals are much more suited to bidirectional controls.
Thanks guys. Makes sense now.
Anyone got a good suggestion for a voltage source instrument that will do -10 to +10?
Mine is just standard 0-10/4-20 ma
Use the motion controller to generate +/- 10 volts
If you are using the HYD02 you should be able to generate +/- 10 volts using the direct drive command. I forget exactly what it is called. If you are using the installed RMC100 then it has a open loop command 'O' that will let you generated +/- 10000 mv or +/- 10 volts.
The point is that the motion controllers have this stuff. Don't make it hard.
yes!!! Or the power to the controller failed.
On a +-10V hydraulic servo valve? Good luck
Servo Valve provides position, velocity, and pressure control.
- Duplomatic DXJ3 Series servo-proportional valve features linear force motor direct driving zero overlap spool. NFPA standard D03 footprint offers integration into standard manifold systems, and neutral fail safe position provides simple control. Operating up to 5000 psi with flows to 10 gpm, DXJ3 incorporates on board electronics that operate on ±10 V or 4/20 mA control signal. Maximum response time is 12 ms with <0.2% hysteresis through closed loop LVDT.
Not sure what exactly you are trying to do or what the problem is but if you are looking for a +/- 10V source you can control just haywire up a PLC and and analog output card, pretty much any of them can be configured for +/- 10V.
What exactly is your problem?
Good day guys, am new here Am using a 1765-Of8 analog output card to sent 0-5v signal for a remote setpoint to a temperature controller of 1-5v...
1,716
IM trying to find a cheap way to read system voltage using a 0-10 vdc input. my working voltage range is from 10-20 volts. Is there a voltage...
4,515
What would be a safe distance between Analog cables (4-20ma)and 120 & 480 volt multi conductor cables laying in a 12" or a 18" Ladder Wire Tray...
6,809
Can a voltage analog output be used on a device where a poteniometer normally goes? Ie, I have a DC drive that only accepts a poteniometer and I...
30
9,211
R
We would like to pick up a sound through a microphone into an analog module. The available analog is 0-10 volt and the ideal is to use it. Does...
5,632