110 VAC audible annunciator
XtremeIN
Jun 2005
Indiana
217
As the title says I am looking for an Audio Alarm. The ones we use normally are 24 V, but I need a 110 VAC one. Automation Direct has some 22mm units, but they are 80db at 10 cm. I was hoping someone had some suggestion for one that has a better range.
Micheal
Allen-Bradley 855P-B10ME22 (100 dB) or 855P-B10LE22 (105dB). The first one is a 45mm device and the second one is a 60mm device, but both mount in 22.5mm holes.
BTW, the sound reference levels are for 1 meter for these devices.
I will probally go with the AB due to the fact the customer has required AB. It will include a SLC 5/05, Panelview, SMC-3 soft start, circuit breaker, E-stop......
Thanks,
Micheal
As a side note, does anyone make a soft starter like the SMC-3?
Quite a few people. I have used the Cutler Hammer IT series with great success. Others include Mototronics and Schneider/Square D. I expect that most manufacturers that supply starters or MCCs can also provide reduced voltage solid state starters.
Good Morning , I have a quick project to do , I know it is not a good practice , but can you put a shielded 120 ac cable in the same...
16
5,321
Hi all, If you are in a corrosive environment, are 110 VAC devices (like relays, contactors, you name it) a better option than the 24 VDC...
2,411
I am having a problem with a 110 vac capactitive prox leaking enough voltage to always light an indicator. This started when the original bulb...
2,634
Hi all, i am working on a project in which i need line filters on the 110 side of the controls. my search for line filters gave a wide range...
3,018
Hi All, I do have a project using FX5U-32MR/ES PLC & GS2110-WTBD-N HMI. I am using GT Designer version 1.109P. However, there is an error during...
1,453