I am looking at a 1305 drive connected to a PLC5 via RIO. The drive is working and I was able to get a functional HIM working on the drive as well.
I see O:151/4 is forward and working as expected
I also see O:151/5 is reverse and the bit does come on in the PLC as expected. When /5 is made /4 is not and vice a versa.
However the drive always runs forward.
I know on newer drives you can block out reverse, but I am not seeing in the manual how this would apply to a 1305 drive via RIO.
I saw parameter 94 had a direction mask but again, I am not sure if that is where I should be looking.
Any advice would be helpful thank you.
Solved
Since the drive was working I came back to Parameter 94. I decided to compare this MASK with Parameter 92 (Logic Mask) and Parameter 95 (Start Mask).
Parameter 94 (Direction Mask) had 00000000
Parameter 92 (Logic Mask) had 00000100
Parameter 95 (Start Mask) had 00000100
Each bit represents allow or deny control for an adapter. The third bit in this case was Adapter 2. I matched the Mask for direction to Logic and Start masks and reverse worked as expected.
Hopefully this helps someone else down the road.
Thank you for the followup !
These drives used masking functions to allow you to mix control modes and limit some of them. I've done systems where the PLC couldn't reverse the drive, but the local inputs could (for maintenance of a supervised mechanism).
Hi Everyone, We do have several cabinets with SLC5/03 CPU's and two SCANport modules, each. 5 ports are being used, communicating with 1305 VFDs...
2,502
Hi all. I am currently on a project or updating a panel with a slc 5/04 processor controlling 3 1305 drives via a 1203-sm1 SCAN Port. The company...
2,289
Good afternoon, I have an AB 1305 Frequency Drive with an HIM module on it. Normally, after it runs a part, it says "Stopped +0.00 Hz". What...
2,989
I have an allen bradley 1305 vfd that is currently in use with a slc 500 and provides two speeds by closing relay contacts with the plc on 15 16...
1,929