1400 modbus to VFD
atvracer
Jan 2015
Oklahoma
hello
im trying to control 3 G3 Dura VFD with a AB 1400 using MODBUS RS485RTU
this is my 1st time I've played with Modbus on a AB and using MSG
what i want to do is all 3 drives to run independently from each other on off speed also i want to be able to monitor the load
here is a little file i'm using to test with 1 drive
43332 run
48460 load meter
i'm not 100% if its my program or wiring or VFD setup
thanks for your help
At first glance the program looks OK.
Are you sure the target drive is set for Modbus Slave ID 3 ?
What is the physical wiring like from the Channel 0 port to the drive ? Usually the 1763-NC01 cable is the way to go.
You have correctly set the port for "No Handshaking (485 Network)" to use the RS485 pins 1 and 8 on the Channel 0 plug.
On RS485 systems, Rule #1 is always to swap the data wires and try it both ways.
I would test this by switching the port back to RS-232 and connecting up a PC as a Modbus RTU Slave tester.
Chipkin Automation's Modbus Parser and Modbus Scanner are great tools, but not what you need here. Do go download their "Modbus for Field Technicians" booklet.. it's outstanding.
There are a handful of Modbus RTU slave simulators on the market, but I like the simplicity of the Win-Tech ModSim program.
http://www.win-tech.com/html/modsim32.htm
thanks i download modbus sim got it running on a different computer
with the sim off line and the 1400 and the VFD on nothing happens but when i get the sim online as the same device as the VFD #3 the VFD will start working runs stops from the 1400 N7:0 and the sim will update what the 1400 is doing. as soon as i disconnect the sim nothing works so i do have a setting off somewhere by where
thanks
I was suggesting switching to RS-232 for testing with the simulator, then switching back to RS-485 for testing with the drive.
Describe in detail how you have this wired up, because I can't picture how you could have both the drive and simulator connected at the same time.
So, here's my hardware: Micrologix 1400 controller Mitsubishi E740 Drive I'm communicating via the 1763-NC01 out of Channel 0 on the Micrologix...
4,936
Hi, I'm having an issue with a mircologix not transmitting out. The current setup is a mircologix 1400 connected to a Guardian 100 Radio...
123
I want to learn about modbus communication and I saw on another thread about inexpensive modbus relay units so I found it on Amazon along with a...
46
7,298
I have a spare Micrologix 1400 Series B I bought used on Ebay awhile back. I had thought of it as a spare PLC for my train project but I screwed...
1,277
Good Day! Would anyone be able to explain what is happening with the COP's and MOV's in this Modbus poll routine? If anything I am confused by...
1,740