16#0203 error code
Apr 2013
Harrodsburg, KY
I can not figure out how to get rid of this error
I have a L63 with a ethernet card in slot 1
slots 3-16 are as follows:
Slot 3 IB32
slot 4 OW16
Slots 5-11 IA16
Slots 12-16 OA16
This is some kind of communications time out error that will shut down the project and intermittently restart and shut back down.
I have read all i can find - no answer that helps
any a/ all thoughts appreciated
Welcome to the forum, Len.
#0203 is a fairly ordinary connection error, so more info is needed to solve the problem.
Is this a new project with new hardware, or an existing machine that has developed a problem?
Let's focus on the blinking I/O module lights.
Are the failures really "intermittent", or are they regular and repeating ? In other words, does the system ever go into run mode and stay there for more than a few seconds ?
starting point is the hardware. Customner purchased hardware and controls from existing surplussed operation.
L63 controller, with three cabinets of control logix.
I have reconfigured their cabinets to match their operations and added IA16 and OA16 modules into their racks.
System ran for a few hours with limited program - simple motor run sequence and scanner reads.
Approx 2 hrs into run, system shut down and the output cards started flashing green OK on the face.
The error code did not cause a system fault as the cards were not configured to create an error on the controller.
Currently there is a 10 min auto restart that causes the system to start and trip
I previously unplugged all and reinstalled everything, the hardware remained stable for 3 days with out motor run circuits installed - all was hardwired while i tested and looked for answers.
I reinstalled the motor run circuits and all was fine. I started further programming and the system failed again.
i can discover the following cards with out issue
slot 1 - Ethernet
Slot 3 - IB32
Slot 4 - OW16
Slots 5-11 IA16
When I attempt to discover any of the output cards in slots 12-15 the system states the card is faulted 16#0203
this appeared to stabilize with an extended RPI of 100ms, this was an incorrect observation
I can not add an OA16 output card to this system. The OW16 configures correctly.
Can anyone please help me?
Exactly what do you mean by "discovering" a module: do you mean browsing with RSLinx, or creating a module in the RSLogix 5000 I/O tree, or something else ?
There's no reason a particular type of discrete output module wouldn't make a connection.
The unknown age and provenance of the hardware makes me a little uneasy. Have you audited the modules for the "Atmel 64" issue from a few years ago?
Your description suggests that the controller is not faulting or clearing the user program, but rather losing the I/O connection across the backplane to the I/O modules.
ControlLogix backplane connections are generally very stable, so intermittent failures suggest bent pins, a defective CPU, or a defective backplane.
in control logix5000
I/O tree project configuration of all modules
I can attempt to put the 1756-OA16 any point in the rack and it will have a 16#0203 fault.
All other cards in slots and "discovered" by the system run and the I/O indicator is "OK"
"create" a 1756-OA16 slot in the rack and the I/O indicator shows "I/O not responding" and the card properties indicate a 16"0203 comm fault
OK, I pulled the CPU removed the battery, let it sit overnight, reinstalled the battery, downloaded the same program, all OA16 cards are being seen and I/O is "OK" with no green flashing "OK" indicators on the 1756-OA16 card face plates
can anyone explain why the comms fail?
Hi I have been knocking my head against the wall trying to figure out why these two plcs won't talk with Produced and Consumed Tags data. The...
497
Hello everyone, I am trying to set up some produced/consumed tags between two controllers. Here is the current setup that I have: PLC #1 Slot 0...
18
10,769
Hi everyone! I am trying to connect a Flex I/O with one 1794-OW8 to it to a CompactLogix 1769-L24ER via Ethernet. It all went well except that...
2,632
I have an Etherenet/IP to Ethernet/IP gateway module by Anybus that act to segragate two EIP networks. On one side is a L71 processor running...
4,610
Hi all, I am a newbie with RA system. Currently I have SoftLogix and try to connect it to talk to the Ethernet/IP module, 1756-ENBT, and IO...
4,828