1734-IB*S Test Output Status

whiteazz

Member
Join Date
Dec 2003
Location
epworth, iowa
Posts
8
In the 1734-UM013 appendix A it shows how to monitor a status bit and then use that bit to trigger a message to retrive the error. I can't find a status bit for the test output that could be used to trigger a message to retrive the error for the test output. Does anyone have a idea on where to look, or a simple way to do this without reading the status of each individual test output on every IB8S module.
 
Last edited:
As far as I rememeber Test Outputs are standard outputs, they don't have built-in diagnostic like safety In/Out have
 
Answer to question

The status of the test outputs can be monitored in the same fassion as the Pt Status's. When configuring one must configure Pt. Status-Power-Muting-Test Output instead of just Pt. Status, for the Input Status; under Module Definition.

🍺
 
Pt. Status-Power-Muting-Test is only required when you set Test Ouptut as Standard outputs
When you use them exclusively for pulse test, this selection is not required
 

Similar Topics

My question is regarding the number of Test outputs vs the number of inputs in a module. In the case of a 1734-IB8S card, there are 4 test...
Replies
5
Views
1,308
To get values from an Allen-Bradley 1734-VHSC24 module, which is a high-speed counter module for CompactLogix PLCs, you typically use software...
Replies
0
Views
67
Looking at installing point io, with a 1734-AENTR communications adapter and ten 1734-IT2L modules. In IAB it installs a 1734-EP24DC after every...
Replies
1
Views
97
Hi everyone, new to forum. Since very long time i having issue with 1734-AENT module, after some period of time its keep stuck in error (simmilar...
Replies
28
Views
1,378
I am trying to use the 4-20 mA signals from a device whose user manual says that it outputs "isolated 4-20 mA". I only have spare PLC inputs in a...
Replies
3
Views
281
Back
Top Bottom