Hi, I have a problem with the scan time of my allen bradley 5/05. The scan time is now aboput 13 ms. This scan time is to long for my purpose and I want to use a STI, selectable time interrupt with my Hi Speed Counter Card 1746-HSCE. I want to read the accumelated count I:e.1. Can annyone tell me if this is possible and how I have to do this? Thanx Feike
 
How to set up STI

Open the processor status display (under Controller in your project tree). Go to the STI tab. Set the "Setpoint" to the interval you want the STI ladder scanned. Make sure you understand the timebase is *10ms unless you set the "Resolution Select Bit". Enter the "File Number" which will contain the STI logic. Create the STI ladder file, and move your logic there. Download. (Note: you can do this online if you create the ladder file first). Try to keep your STI logic as efficient as possible. Your regular program scan time may now be more erratic than before, depending on how much code is in your STI and the "Setpoint" frequency. This may adversely affect PIDs and other scan time critical code. Understand that the processor will stop IN THE MIDDLE of its regular program scan to execute the STI logic when the time comes. Therefore the STI program will run asynchronously to the rest of the program.

Paul Cunningham
 
Last edited:
You cannot use an STI with the 1746-HSCE. It runs at it's own scan time dependant of and on the processor.

I think a 5/05 runs this card at 45ms.

You must use the 1746-HSCE2 in order to use an STI
 

Similar Topics

Can anyone tell me please if there is a way (exept an IMM instruction) to read the accumelated value (I:e.1) of the Hi speed counter 1746-HSCE...
Replies
9
Views
2,812
I had a 1746-HSCE go suspected bad. have to swap the card in the morning. Other than dip switch settings is there any configuration to do?
Replies
1
Views
1,025
Hi there, I have a machine where was a servo with extra encoder. That encoder had resolution 100ppr/5V. We did replace complet servopack (...
Replies
0
Views
948
I have a SLC 5/05 processor and I am trying to reference an output from a High speed counter card to be used elsewhere in the PLC. The output...
Replies
1
Views
1,639
I am upgrading HSC modules and have some questions. I can't attach the manuals for reference as they are too large. 1746-HSCE uses M0:e.1/4 for a...
Replies
0
Views
1,653
Back
Top Bottom