1747-aic
godfrey
Apr 2002
Charlotte, NC
412
Is there a user manual on the 1747-AIC? I have one for the 1761-NET-AIC. In terms of applications, how does the 1747-AIC differ from the 1761-NET-AIC? I need to connect a PanelView 1000, a SLC 5/03, and a SCADA computer together. Can I use either AIC?
A 1747-AIC is an Isolated Link Coupler. Ideally, every node on a
DH-485 network would have one(unless you just have a stand-alone SLC). It provides electrical isolation from the port on the SLC and the rest of the network, and also gives a port to plug a PC into, allowing the SLC to retain connection to the network.
A 1761-NET-AIC is a RS-232(DH-485) to DH-485 convertor. It provides a connection point for the standard AB DH-485 network as well as 2
RS-232 ports for connection of devices that are capable of RS-232(DH-485) communications.
To sum it up.......
The 1747-AIC is a drop point for a DH-485 network, that provides electrical isolation.
The 1761-NET-AIC is an RS-232(DH-485) to DH-485 converter.
Each has it's own application. There is a lot more information over at the AB website.
If your PV 1000 and SCADA connection(like a KTX card) are DH-485 then you will probably go with the 1747-AIC's.
If the PV is an RS-232(DH-485) and you dont have a KTX card and want to connect the SCADA through RS-232, then you will probably use the 1761-NET-AIC's. One thing to consider; The 1761-NET-AIC, being a converter and pumping data through RS-232 is going to be slightly slower.
Post with the specifics of what you have: Is the PV RS-232 or
DH-485?, Does the SCADA PC have a KTX card? Is either port of the SLC used, other than what you are discussing here?
Thanks for the info. Here's what I know now.
I am designing a panel as per job specs and customer plans. The parts are not purchaced yet. The PV and SLC 5/03 are in my panel. The customer's drawing shows a 1761-NET-AIC with three lines coming out of it. One to the PV, one to the SLC at port 1 and one to the SCADA. Each line is marked DH-485. I don't know by what port or hardware the SCADA will tie in. I will ask them Monday. The drawing also shows port 0 of the SLC going to something called a SCADA PAK.
With this much info, can you tell me more.
I think I can guess the designer's intent here. Check out page 3-5 of the 1761-NET-AIC User's Manual for a similar (though yours is simpler) diagram.
You'll use just one 1761-NET-AIC. From that device, your cabling will be as follows:
Channel 1 (6-pin Phoenix RS-485)
1761-CBL-AS03 or -AS09 cable to the Channel 1 plug on SLC-5/03 CPU.
Channel 2 (8-pin Mini-DIN RS-232)
1761-CBL-PM02 to RS-232 port on "SCADA computer".
Channel 3 (9-pin DB-9 RS-232)
Straight-through RS-232 cable to DH-485(RS-232) port on PanelView 1000
+24 VDC power to the power screws.
This will give you the minimum of wiring hassle, even though you need to buy two A-B cables.
The PanelView must be one of the units with DH-485 protocol implemented on RS-232 type electrical connections. The part number must end in "9", such as 2711-K10C9 for the color 10" keypad terminal.
This will give you a small 3-node DH-485 network. Traditionally the SLC-5/03 is Node 1, the PanelView is Node 2, and the computer is Node 3.
This leaves the Channel 0 port of the SLC-5/03 open for a different communications protocol, most likely DF1 over a modem of some kind. "SCADA PAK" sounds like Intellution to me, but if it's not your scope of supply just leave the Channel 0 port empty and at default settings.
I have the following Items connected for DH-485 per the drawing. SLC 5/03 HMI: Automation Direct EA9-T10CL+13Y19B054 1747-AIC #1: connected...
3,050
Hi all. i need an a advice. I use PV800 -T4T or T7T ( to a replace for an old PV550 ). But I have a problem " create communication with PLC...
1,730
Hi, I have SLC 5/03 with 1747-AIC (DH485) modules. Original HMI was PV550, this HMI was replaced to a PanelView 800 (2711R-T7T), communicating is...
1,243
Hi everyone, I have foolishly taken the task to upgrade our older style Proface HMI's from GP377-SC41-24V to GP4401WW. I was able to convert the...
994
Hello There, In my control panel, port 1 or RS232 port of a 1747-NET-AIC is connected to a compactlogic l32e and DH-485 or port 3 of the...
2,000