1747-SN Accessing diagnostics?
Join Date
Feb 2008
Location
Walnuc Creek, CA
Posts
31
Hello,
I'm working on a project with a SLC 5/04 accessing RIO through a 1747-SN. The RIO Scanner module has 2 diagnostic LEDs for the COMM STATUS and FAULT. I'd like to be able to throw an error if the RIO commnunications link goes down. Are the COMM STATUS and FAULT diagnostics accessible for the programmer? Anyone who can point me in the right direction, I'd be very thankful.
Thank you in advance.
Hi
The scanner's M1 file words 0 to 47 contains the status of all devices on the RIO link. See the user manual page 4-23 for details. In particular: word 0, word 10, and words 12 to 15.
The manual can be found here
Hope this helps.
Yeah, what Kieth said....Use the M1 status words. Take it a step futher and show a network layout of each device on RIO and the current comm status of each device. I did that on my last install with a SLC 5/05 and it worked well.
Similar Topics
hello I am getting a 57h fault - Specialty I/O module has not responded to a lock shared memory command within the required limit. Fault randomly...
Replies
2
Views
100
We are in the process of upgrading a controls system. The existing system is a SLC500 with some IO cards and a 1747-SDN module communicating to a...
Replies
5
Views
562
se me desprendieron los cables del cable usb quiero soldarlos pero no se como van los cables si alquien me pudiera proporcionar una foto o como...
Replies
1
Views
412
Hello, I've got a project where I need to get information from two ABB ACS880 VFDs onto the plant operator's screen (or alternatively, onto...
Replies
23
Views
2,642
Hi Newbie here :yeah: Can one of you experts help me with setting up a simple BTR and BTW to just test 4 analogue inputs 4-20ma (1974-if4i)...
Replies
11
Views
1,007
Back
Top Bottom