1756-L71 Redundant Download

stretch_af

Member
Join Date
Mar 2011
Location
Drinking in Wisconsin
Posts
69
I have read through this pub: Rockwell Automation Publication 1756-RM010M-EN-P - November 2022

I have questions. The procedure in the pub above is more for updating firmware, not specifically program updates.

We have 2 redundant chassis with L71 processors, running firmware 24.052. EN2TR/C is at 10.007. RM2/A is at 20.007.

What we need to do is perform a download to add a remote I/O rack to the tree.

Is there a way to download the updated program to the secondary?
Then initiate a lock switchover to update the primary?
Or do we need to bite the bullet and take the system down for a few minutes?


Thanks
Justin
 
We could have added a ControlLogix chassis as a remote I/O while online. We were trying to save some $$. We have a 1769-AENTR on the shelf that we are trying to use. We could add the 1769-AENTR to the tree while online, just not any IO attached to it.
 
We could have added a ControlLogix chassis as a remote I/O while online. We were trying to save some $$. We have a 1769-AENTR on the shelf that we are trying to use. We could add the 1769-AENTR to the tree while online, just not any IO attached to it.
Ah, interesting. I know you can't add IO to a CompactLogix while online, so maybe that's part of the same limitation.
 
1769 IO is not supported by the ControlLogix Redundancy.
There are multiple technotes about that.
QA26592 is one of them.
 

Similar Topics

Hello, I have a pair of redundant 1756-L71 controllers rev 24. These controllers currently have produced and consumed tag interfaces to 3 other...
Replies
2
Views
172
Hi All, We have a number of old discontinued 1756-L1 PLC systems that we are trying to support but recognize that we need to start preparing to...
Replies
5
Views
975
Two days ago I used Control Flash Plus to upgrade the firmware on a 1756-L71 controller from v20.13 to V35.12. The upgrade aborted soon after it...
Replies
8
Views
1,131
I have followed several videos and tutorials that suggest when using the MSG function to enter 2,xxx.xxx.xxx in the Path box in order to connect...
Replies
11
Views
1,390
Hi All, I'm trying to upgrade from 1756-L61 to 1756-L71 but I keep getting an error 25299-0. Is there anything that need to be complete to be...
Replies
3
Views
1,836
Back
Top Bottom