1756-M02AE ?....Error code 11 returning on execution of MSO cmd
CntrlFreek
Aug 2014
Pa
Hello all,
Im having an issue with a 5 axis ream wrapping machine. Clogix 5561 cpu, 3-1756-M02AE analog servo modules, Indramat ecodrives, indy ac perm magnet servos w encoder fdbk. We have recently moved the machine from another state and installed it in our facility. Upon initial startup of the machine all was well. The drives all enabled, the axes all homed, machine cycled well. Over time and some tweeking of mechanical issues the machine would not always home as it should. What i discovered is that when the MSO command is executed an error 11 "servo axid not configured error" returns in word (Ax02MD_Command.MSO.ERR). With that said i thought maybe the servo module somehow lost its configuration, therefore simply re-downloaded the same project i was currently online with. The MSO executed after reset and returned the same error. What confuses me even more is the fact that i can reset the module from the I/O properties form, issue motion direct commands from the mdc form, read accurate position fdbk/velocity from the axis, the servo module/servo drive show no physical axis faults. Can someone please heeeeeelpppp me. im lost. thank you in advance.
regards
a QUICK search of the Knowledgebase turned up something which MIGHT be helpful - or at least might get you thinking in the right direction ...
37216 (Access Level = Tech Connect)
notice that there is a difference between the operation between firmware versions 15 and 16 ...
based on this alone - I'd be checking connections, cables, and finally feedback devices for something along the lines of "loss of signal" ...
hope this helps ... good luck with it ...
What version of RS5000 are you using?
IF the Motion Direct Commands all work then there is something in your code that is not treating the MSO command correctly
Eg you are trying to issue a MSO while the axis has an active fault
Make sure Ax02MD.axisFault = 0 AND Ax02MD.ModuleFaults = 0 before letting the MSO execute
Sorry for my very delayed response and thank all of you for your responses! Turns out the drive was the issue. This was not so obvious because the drive would enable, however would not throw a fault due to the fact that the I/O board was bad. The drive was only doing what it was told to do........nothing! lol maybe i over thought that one!
Thanks again guys!
Dear All: I have the flashing red light on the FDBK indicator. The manual said that it means: The axis servo loop error tolerance has been...
644
im pretty new to motion controls but i have been trying to figure out how to control this powerflex 525 with the servo axis module 1756-m02ae per...
839
I have this module being used with a Controllogix 1756-M13/A. Using RSLogix5000 Version 8 I have an Exclamation mark on the I/O Configuration file...
3,110
Hi guys, I need to calibrate two encoders on a plank edger. One is on an infeed belt, and the second is on the rolls and outfeed belt. This is on...
3,505
Hi, I have a big problem with an 1756-M02AE controlLogix module. I replace one of this with brand new one ( 1756-M02AE , same class and same FRM...
3,830