1761-NET-AIC Setup
The Plc Kid
Feb 2009
Macon, Georgia
3,233
I am about to replace a pv 900 standard with a pv plus 1000 and moving from rio to a dh485 connection. The plc is a slc 5/04 so i will be using a 1761-net-aic to connect the slc to the pv over dh485.
Looking over the documentation to the net-aic it is not clear to me if i need and external power supply or not. The manual gives reference that it is not needed when connected to a micrologix but that is about it. I think i do need 24 volt power to it which i can get from the slc chasis powersupply as there is nothing on it now.
I just wanted to double check if i am correct or not?
If the Panelview is DH485 (the DB9 type) then you won't need the AIC at all. You just use a straight through cable to connect the SLC to the Panelview. The only connections you need are on pins 2,3 and 5. (Assuming its a 1:1 connection)
Otherwise I believe you need the external power if you aren't using the 8 pin connector on the AIC.
you can power NET AIC from the chassis however the power available at the chassis is limited. check the power requirement of all your I/O modules make sure there is enough left for NET AIC, otherwise you need an external power supply. There should be a switch in the AIC to determine where power is comin from, either from cable or external. Check this switch.
Hello, currently I have a micrologix 1200 (1762-L40AWAR )connected to an HMI panelview 600(2711-T6C3L1X) via the 1761-net-aic module, I want to...
1,804
I've attached pics, below. I'm in the field right now an am trying to communicate to the Micrologix 1500 through the 1761-NET-AIC (Ugh!) to...
1,956
The manual for the 1761-NET-AIC shows connecting a PC to DH485 network with a 1761-PM-02 cable. Is this done using a DF1 driver set to...
1,073
A customer of mine has a ML 1500 LRP connected to a Net-AIC+ via the mini din connector (CH 0 of plc to port 2 of AIC) from this AIC then connects...
1,794
I have a bunch of ML1000 PLCs on a DH485 network using 1761-NET-AIC modules and we are replacing the ML1000s with ML1400s. Once all of the...
2,010