1761-NET-ENI Explosion Hazard
alive15
Oct 2015
Montgomery, AL
724
Good afternoon,
I noticed on my 1761-NET ENI a label that says not to disconnect or flip the switches in a hazardous area due to an explosion hazard. Currently the net eni is connected to a PLC and a Cmore HMI. How does flipping the switch or unplugging the cable b/w the net eni and the PLC cause an explosion hazard? Just being curious. Thanks.
I imagine it would have to do with potential arcing/sparking... probably a very very low possibility of anything happening but they are covering their bases. Sort of like when bakeries add a small amount of an allergen just so they can label the product as containing the allergen to avoid contaminated batches causing liability issues.
Just a guess though. Others may know more
It's a warning if the product were to be used in a potentially explosive atmosphere. The potential sparks from those actions are less than the static spark after walking across a carpet. In a normal atmosphere there is virtually no chance of the spark causing anything hazardous.
Look at things this way.
you go into your house and smell a gas leak. at that point you should leave your house immediately with the door open and call the gas company. No problem.
what you do not need to do is create a spark which can ignite the gas vapors in the room, and cause an explosion.
you can obviously create a spark by striking a match, using a lighter.
you can also create a spark by unplugging / plugging in an electrical device, turning on a light switch, or other similar things. the manufacture of devices like that ASSUME that there is nothing in the area that will explode or catch fire. they are not made to keep out dangerous gases and the things I discuss below. That's why they place the warning. you need to know the area where the device is to be used.
the manufacturer is stating that there might be enough potential energy when you flip the switch or unplug / plug in the device to create a spark. that spark may have energy in it to cause gas vapors, dusts, of fibers to ignite and create a fire or explosion.
Hazardous locations are defined by a class and division.
Class 1 - flammable gas, vapors, or liquids.
Class 2 - combustible dust.
Class 3 - ignitable fibers or flyings
Classes are also defined into divisions.
Division 1 - The area has material in the environment at all times during the manufacturing process and for a period after manufacturing has stopped. some areas never stop having the materials present.
Division 2 - the area has the potential for an explosion during an abnormal situation or in an emergency.
I have worked in class 1, div 1 and 2, Class 2, div 1 and 2 for 12 years.
creating a spark in these areas is very serious.
We had devices that would detect a spark 1/4 mile away. NO JOKE. our deluge system would flood the area within 23ms when a spark was detected with 110 gallons per minute per nozzle.
in these areas, you would need intrinsically safe barriers to prevent such a spark.
I hope this explaination helps,
james
The warning is on many devices that can cause a spark when connected or disconnected to a power source.
It's particularly prominent on these network interface modules because of the +24V power supply option via the Channel 0 connector and the internal/external power supply selector switch. Both of those have the potential to create a small spark when they are connected or disconnected, and they aren't the usual permanent power connection devices.
The device probably has Class 1, or 2, Div 2 approval and that is why the warning is on there. Nothing to worry about unless you're using it in a potentially hazardous area.
"Hello! Good day! Excuse me, I have a question regarding the 1761-NET-ENI. RSLinx has already detected it but it's not connecting to the PLC...
149
Good afternoon guys, does anyone recommend a direct replacement part for Allen Bradley's 1761-NET-ENI devices? We have a lot of these in our plant...
1,011
Hello, currently I have a micrologix 1200 (1762-L40AWAR )connected to an HMI panelview 600(2711-T6C3L1X) via the 1761-net-aic module, I want to...
1,796
I have decided that instead of upgrading the drives & plc at the same time on my project i would just do the drives for now as just getting them...
23
9,031
Our company has many of Rockwell's beloved NET-ENI modules to get SLC 5/03's onto our network. They have the issue of faulting out if more than 3...
1,925