1761-NET-ENI with RSLinx Enterprise
ENV Prog
Apr 2007
Atlanta, GA
I wonder if anyone has seen this issue. I have used the NetEni module successfully many times, but this my first time using it with RSLinx Enterprise.
The module is connected to a Micrologix 1500 and it has a static IP address. I also have a PanelView plus 700 with a static IP connected to the subnet. RSLinx sees the PanelView and the Micro 1500, which is the way it should work, ie: the NetEni effectively disappears when properly connected to a Micrologix and the NetEni IP address shows up as the PLC. So everything is fine there.
Using RSLinx Enterprise only the NetEni and Panelview show up. So I have attempted to use the NetEni as the target device anyway and of course I get an unsupported device error.
If anyone has used the NetEni with RSLinx Enterprise I would greatly appreciate your insight.
In Linx Enterprise, have you added the 1500 as a 'Net-ENI Connected Device'?
You don't just put the PLC there in the Communications target tree, or the Net-ENI. You have to add the actual target device as a Net-ENI connected (PLC/SLC) device.
Thanks rdrast, that was good info. I had not configured the connected device.
It was not easy to do though as the Ethernet browse occured every time I clicked on the Ethernet driver, and my PLC device would keep being replaced by the Net-eni.
For anyone else with this issue I finally found Knowledgebase article id #29966 that addresses this browse/replace issue.
Cheers!
"Hello! Good day! Excuse me, I have a question regarding the 1761-NET-ENI. RSLinx has already detected it but it's not connecting to the PLC...
156
Good afternoon guys, does anyone recommend a direct replacement part for Allen Bradley's 1761-NET-ENI devices? We have a lot of these in our plant...
1,014
Hello, currently I have a micrologix 1200 (1762-L40AWAR )connected to an HMI panelview 600(2711-T6C3L1X) via the 1761-net-aic module, I want to...
1,797
I have decided that instead of upgrading the drives & plc at the same time on my project i would just do the drives for now as just getting them...
23
9,033
Our company has many of Rockwell's beloved NET-ENI modules to get SLC 5/03's onto our network. They have the issue of faulting out if more than 3...
1,926