1761 NET ENIW ethernet interface with SLC5/04 DH485 port

ahsan1820

Member
Join Date
Jan 2012
Location
karachi
Posts
22
Dear,
I have to communicate my SLC 5/04 CPU channel0 ,configured as DH485, i have an ethernet interface 1761 NET ENIW. I have read how to configure this 1761 NET ENIW via PC comm port ,using ENIW configuration utility.
I want to communicate in the following manner
PC ethernet port to ENIW ethernet port using ethernet cross over cable and RS 232 port to SLC channel0(configured as DH485) via a 1761-CBL-PM02 series C cable.

But please tell me if there will b any issue with channel 0 of slc is configured as DH485 and ENIW has rs 232 port.
 
I am doing this exact same thing on my desk at the moment.
I do not think you can use DH-485. Ch0 on the SLC 5/04 is RS-232 (An electrical connection standard), on top of that electrical connection you can use DH-485 (A communication protocol, not electrical) or DF-1 (Another communication protocol, not an electrical specification).

The Net ENI module has the ability to translate Ethernet/IP into and back from DF1 only.
http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1761-um006_-en-p.pdf
This is the manual for the net eni. It does not contain any references to DH485, but it does contain references to DF1. That is a simple indication that DH485 is not a supported protocol.

http://www.plctalk.net/qanda/archive/index.php/t-11382.html
This thread indicates you will need a different module entirely, one that speaks both DH485 and Ethernet protocols.

Perhaps something like this device.
http://www.prosoft-technology.com/Products/Gateways/EtherNet-IP/EtherNet-IP-to-DH-485-Gateway

But that is all I know.
 
Last edited:

Similar Topics

please help me. i am trying to take to this by using ENI Configuration Utility, but i cant load when i try eni ram or eni rom. i am using...
Replies
0
Views
1,438
please help me i need to know how to set this up step by step, thia is what i have ! slc 5/04 1761 net eniw rslinx pro ver2.2 iam using...
Replies
13
Views
10,267
Can anyone help place a message in a string data file so that it can be sent via email to the desired location.Any code using RSLogix 500 will be...
Replies
13
Views
2,289
i connected the device to a 1500 PLC, and it is working fine ( i can load and download programs to and from the PLC using RSlogix ), problem...
Replies
47
Views
9,391
Need help setting up the MicroLogix 1500 to send emails.Also need to know how store a string in a data file.
Replies
2
Views
2,271
Back
Top Bottom