1762-IF2OF2 COM connection
Nin_CaLs
Dec 2021
Philippines
Hi Sirs,
Good Day.
I have a simple questions/clarification regarding the connection of "negative channel" and "com" of the analog input module 1762-IF2OF2.
1. Should the "COM" be connected on the negative dc power?
2. Is it okay to jumper all the negative connections?
3. Is my expansion module slot arrangement okay? Or is there preferred slot positioning based on the module. (which should come first and last)
Please see attachment for the wiring diagram and advise for any concerns.
Appreciate for all your help. Thank you.
1. Should the "COM" be connected on the negative dc power? Yes
2. Is it okay to jumper all the negative connections? You can check with your meter but I think they are inside the module already
3. Is my expansion module slot arrangement okay? Or is there preferred slot positioning based on the module. (which should come first and last) Looks good to me
Nice drawing
Edit: Also check your dip switches and make sure they are set correct for the IF2OF2, they will need to be set to V or C depending on your application
I have a Moog hydraulic servo valve that operates a cylinder that moves up and down. I have the 1762-if2of2 hooked up to it and sending the 4-20ma...
2,631
I was trying to use a Micrologix 1100 and a 1762-if2of2 Analog IO card to demonstrate A/D and D/A conversion. Simple ladder logic Enter a value...
3,889
Hey all, Been working on a little project using a Micrologic 1100, Just added this 2-in/2-out analog module (1762-If3Of2)to my project, and a...
2,200
So I got my ML1100 up and running last night, and tonight Im trying to connect an analog in/out module 1762-IF2OF2. The problem is that the green...
2,263
Hi guys, I'm working on an article about the bit resolution and precision of a 1762-IF2OF2. I know it is 12 bit which is 0-4096 and that the data...
3,273