1762-ow8 micrologix 1200 plc
rushme
May 2010
pune
i have the plc 1762-ow8 micrologix 1200 plc and a slave having rs 485 interface. how do i connect the slave to the plc. the slave is quasar meter. reply soon its urgent:confused:
I am making the assumption that the slave device you have needs to talk modbus. If this is so, you will need an RS485/RS232 converter (I don't think the ML1200 supports RS485 directly from the 8-pin mini din socket?)
Set the port for modbus MASTER (ensuring the communication protocols are set the same as your slave device - baud rate/parity etc) then use MSG blocks in your code to interrogate the slave device (there are plenty of samples of Micrologix code set up for modbus).
Not sure what the reference to the 1762-OW8 was related to (unless i have totally misinterpreted your setup)...
Hope this helps.
Rob
Does anyone know what type of thermister for the CJC on a 1762-IT4 thermocouple card? I have searched everywhere and can not find. I can not see...
626
Hi every master,Recently i met a fault about 1762-L40BWA 1,When i get the PLC, The Fault light is lighting, I am not remember the fault message,I...
720
Hello everybody and master,I met a problem about ML1200.It is described as below: 1,When i got this PLC,The FAULT light is lighting, My computer...
1,113
I have 1769-IF4 module and 1766 micrologix 1400 series B controller, when connecting Analogue input in module it's showing maximum values of...
1,698
With the ML1100 being a Legacy product, this is something of an academic discussion. I have an ML1100 with two expansion modules - 1762-IF2OF2...
867