1769 Devicenet Scanner Command Array
minaykha
Apr 2009
singapore
96
Hi Everybody,
I got error code 90 on my DeviceNet Scanner.
I go through manual and found that DeviceNet port is disable and to check the command array.
Can anyone advice me where to check the module command array status ?
Thank.
Are you using a MicroLogix 1500 or a CompactLogix controller ?
The first bit of the Command Word is the "RUN" bit, and the third bit is the "DISABLE NETWORK" bit.
In the MicroLogix, these will be in the first word for the 1769-SDN's slot number. If the 1769-SDN was in Slot 1, for example, the Disable Network bit would be O:1.0/2.
In the CompactLogix, it's a Module-defined tag, similar to "Modul_Name:O.CommandRegister.DisableNetwork"
Dear Ken,
Thank you very much for your useful info.
I am using compatlogix controller and now i can find where is the command array.
see if this helps ... this example assumes that your SDN module is located in Slot 8 on the local bus ...
Hello, I'm trying to replace a 1769-SDN devicenet scanner on a compactlogix system. The issue i'm having is when i replace the scanner and...
1,896
I am experiencing problems with 1769 SDN Devicenet Scanner and i need to replace it by new one . I need in details the steps required for...
2,948
Hello forum members, We are having a frustrating issue (yet again with my favorite network - Devicenet). We have an ABB robot that works with an...
4,023
I have an issue trying to replace a device on a devicenet network. I'm not very knowledgeable about devicenet. Anyway, I've successfully gotten...
26
5,087
Have anyone met this issue that you cannot see the devicenet scanner via RSlinx or RSnetworx? I am using 1769 SDN @ node 1 on compactlogix. For...
11,263