Hey all,
Running into a problem that has us stumped. We are using a 1769-HSC card on a CompactLogix for a Filler Flowmeter, we are trying to SIP and can't get the output to fire on the card itself.
According to the PLC program, the OutputOnMask.0 and OutputoffMask.0 are both ON, which should be firing the output(which is a solenoid valve). According to the HSC manual, both of these need to be on for it to fire the output.
We tried changing out the card to no avail. It had been working until a proximity switch had been adjusted, after that it stopped functioning. We checked functionality of the prox and it is flagging on and off in the PLC itself.
Any help would be much appreciated.
Thanks very much,
Damon
Update:
We finally got it figured out.
It turned out to be a negative setpoint in the HSC itself. It effectively stopped the card from activating the output.
Hope this helps someone else.
-Damon
I'm trying to have one of the outputs mirror one channel of the encoder. It seems possible but can't seem to configure the card correctly. Any...
1,368
Hello: I use the 1769-HSC module in the compactlogix system, the cpu1769-L32E, now I use the 1769-hsc output, but i can't configuration and...
1,694
Hello all. I am having trouble setting up my HSC to count pulses from a prox switch. I have it wired to the prox and I see the .InputStateA0...
1,371
Here is my hail Mary pass I have a wheel that produces 33 pulses per revolution. The RPM of that wheel will be anywhere from 25.21 to 62.7 Pulses...
4,704
Hello all. I have an issue that keeps plaguing me. The system has a 1769-L24ER processor and a 1769 HSC card. I am using CH.0 for tracking...
1,468