1769-SM2 Config
LBT
Mar 2022
Montreal
Hi
Project's PLC is a 1769-L36ERM used with a Siemens LME73 Flame controller. I have to establish communication between these devices thru a 1769-SM2.
I know the Siemens LME (and its Modbus Interface OCI417) is OK as I tested it with a Horner Controller ... all went fine. So the only cause of non-functioning is the config of the brand new 1769-SM2 mounted on my CompactLogix (Slot 1 -> position ok) ...
Anyone has ever used the 1769-SM2 card with this particular Siemens module group or anything else than the PowerFlex "as it is ment to" based on Rockwell help and documentation ?
What Instances have you been using?
(I can't get anything else than Flashing RED LEDs -> "Not receiving comm..."
How did you setup the msg instruction ? ...
LBT
I think your answer is in chapter 5 of the pdf for the SM2. Messaging a Modbus device.
Looks like your flame device can speak modbus is the only chapter that is common between the 2 devices.
So I have a system that is running on DeviceNet. We have been having nothing but problems with it for the last 3 years. I am trying to switch...
1,294
Hello everyone. I'm trying to communicate a Controllogix L36ERM with a 1769-SM2 Modbus module to a Schneider-electric Altivar 312 Modbus motor...
2,515
Hi All. I am trying to relocate a simple MODBUS system from a MicroLogix 1400 (on channel 0 set as a Modbus RTU Master) to an CompactLogix SM2...
1,825
I am using a 1769-L35e with a 1769-SM2 (latest firmware) to communicate with a MicroMotion transmitter (9739MDV) that automatically detects serial...
3,595
Hello!Sorry for my English There are some problems with that module. I have CompactLogix L23E QB1B amd module 1769-SM2. Also I have modbus Slave...
1,536