I sort of remember reading somethimg about using
analog modules in a PLC5 remote rack with
asb module. Does anybody know about this or
is alzheimer's kicking in?
Best to re-read the manuals, in the old days, if I remember right you had to use BTR/BTW but now it may be possible using M files. Do not rely on this Alzheimer head either, I did not look it up.
I think the issue you may have had Deja Vu of, is the location of the analog modules. I seem to recall something long ago that the Analog and Intelligent modules should be the closest to the ASB modules in a remote rack
Ian
There is an article written for the ControlLogix using RIO to 1771 IO that references that an ASB can only handle one message at a time. Reading into this, if you have multiple Analog IO modules in the chassis, then use a "message manager" to coordinate your messaging.
I don't really know if this has any significance on the PLC5, but thought I would just throw it out there on the table.
If you are looking for the refernce, look on the answer center (formerly Knowledgebase). I didn't print the article, but did the attachment. It is titled "DH+/RIO Message Management in ControlLogix"
Hi: I recently tried connecting 2 new single-ended 4-20mA analog inputs to an existing 1771-IFE. The IFE is in a RIO chassis. The values coming...
1,410
I'm having issues saving the individual channel settings on a 1771-IFE Analog card. We recently swapped from 0-10v to 4-20ma transducers. I...
1,016
I have a PLC5 5/15 that use to read a level probe (4-30mA) signal from a 1771-IFE analog input card. The probe has been out of use for probably 10...
3,046
I'm trying to open the BTR/W Setup Screen for pre-existing BTR/W's in Logix5 and getting the warning "no module exist in I/O configuration". I...
6,154
Most of my lunch hour today has been spent searching the forum for help with this issue. While I did get some help from the various topics I still...
4,922