1784 pktx card malfunctioning

rejoe.koshy

Member
Join Date
Dec 2011
Location
kolkata
Posts
195
hi,
I have a scada system in which 6 PLCs are connected via DH+ cable to a pc with a AB 1784 pktx card installed in it. I have configured rs linx but cannot find the online PLCs connected to it. The card is blinking green . What could be the problem??
need help urgently!!
 
Was the card working previously, or are you attempting to set this 1784-PKTX up for the first time with this computer ?

If this card was working in the past and now the DH+ LED is blinking green and the PLC's don't show up in the network browse, then it is very likely that the DH+ wire is broken at some point in the daisy-chain.

The only way to figure out where is to use an oscilloscope to look for DH+ signals, or decommission the network and "ring it out" using a continuity or cabling tester.
 
yes the card was workng fine in the past , but an attempt to download a program in to one of the plcs has triggered this problem..is there any possibility of a baud rate mismatch??
 
i have checked the DH+ cable for breaks but could not find any.To reconfirm my conclusion i subjected the cable to continuity test & the results were in affirmation .
what could be the issue ?? need help guys !!
 
out of six connected processors,4 are PLC-5/40 E & two are SLC-5/04.Channel 1 is used for SLC- 5/04 processors & channel 1A for PLC-5/40 E processors
 
out of six connected processors,4 are PLC-5/40 E & two are SLC-5/04.Channel 1 is used for SLC- 5/04 processors & channel 1A for PLC-5/40 E processors

The node addresses for your SLC5/04's are software configurable, go to channel configuration and change it there.
The node addresses for your PLC5/40 channel 1A is set by dip switches on the controller.
 

Similar Topics

Hi, Previously we used SS5136SD DH+ cards for communicating with Allen Bradley SLC 5/04 PLC utilizing Wonderware free SST5136 DDE server. This...
Replies
0
Views
2,851
I am having some trouble getting a PV+1250 with a 2711P-RN6 RIO adaptor to communicate with a PLC-5/20. So after a call to AB and a lot of...
Replies
2
Views
5,318
I have a 1784-PKTX card connecting to a PLC on a new PC. The old PC was using 1784-KTX. I am now experiencing problems with getting fix32...
Replies
2
Views
2,685
hi guys, hope you can help me out. i'm having trouble enabling a channel on an AB 1784 PKTx card using wonderware's I/O server software...
Replies
5
Views
9,852
I am using AB 1784-PKTX card for DH+ communication of SLC 5/04 and computer with wonderware SCADA (I/O Server). But the installation get conflicts...
Replies
0
Views
5,756
Back
Top Bottom