24VDC Class 2 Power Supplies

ncs

Member
Join Date
Nov 2022
Location
vt
Posts
2
We normally ground the -24VDC side of a control systems power supply. What are you folks thoughts about grounding the -24VDC side of a class 2 power supply?
 
Two articles for reference on this topic from Control dot com

We typically leave them floating. We've experienced fewer problems with analog signals and devices where there is a nearby VFD ground fault, for example. I have one system of about 16 small panels that we commissioned but were built by a subcontractor who grounded the 24VDC common. They were installed in multiple pump stations and water tower monitoring applications. We've had more problems with failed sensors and analog cards at that customer than most of the others we built in house with floating DC voltage. I have since removed the connection from DC- to ground on some of them and it seems to have helped. This is just anecdotal and somewhat subjective support for floating, but isn't really substantial.

In the few cases where we have 240vac or 480vac input to the power supplies, we do ground them.
 

Similar Topics

I have been requested to test this proportioning valve for PLC control of flow/pressure. Dwyer Series SVP Proportioning Solenoid Valve The flow...
Replies
10
Views
421
I have begun using 480VAC power supplies in my panels to keep heat from a transformer out of the panel. This works great if the panel is mounted...
Replies
17
Views
4,144
Good morning, could anyone recommend a 24VDC pulse counter which counts up or down to a preset #? Once it reaches this number, send a 24VDC back...
Replies
3
Views
1,647
UL 508: Any reason I can't supply a 60W 24VDC power supply from 2 legs of 480VAC? Our MechE is asking, it is for a product I don't deal with. My...
Replies
12
Views
5,879
Got a new piece of equipment that has a flow switch on it. But the flow switch is 4-20ma output and we don't have any analog inputs left and the...
Replies
19
Views
5,179
Back
Top Bottom