3 wire npn prox sensor with inverted output?
Bobbias
Jan 2010
Midland, Ontario
233
We have a stamping press with some prox sensors on the die for slug detection and we just ran into a problem where the output from one of the sensors seems to be reversed. We replaced the sensor itself, the cable coming from the sensor, checked other connection points but havent found anything obviously wrong. Does anyone hve any ideas on what could be causing this?
Solved. This problem started before my shift, so I didnt watch the other electrician replace the sensor. When i got there to continue troubleshooting I double checked the model numbers and realized they grabbed a normally closed prox instead of a normally open. After a few minutes tracking down the right sensor, everything was fine.
Lesson: check the full model numbers, not just whether its npn or pnp...
Hi there, I have a 2 wire npn sensor. For example in this diagram: I'm guessing i should connect it to a PLC dc sourcing input as such? Would...
5,223
Does anyone have experience wiring this type of analog pressure transmitter up? It's 4 wires. 3 blacks and 1 green which I assume is earth...
276
Hi everyone, I need some help I new with omron plc. I using plc CP1L. When I do the program it's good and the plc is function as program. But when...
86
Hi there, Trying to get some ascii serial communications working via RS485 (COMMREQ functions). I have attached our wiring for the COM2...
982
What's everyone use for I/O drawings on new installs. I am trying AutoCad Electrical, but can't download it due to a MS Office application running...
1,318