3-Wire Xmitters - Wiring Rqmts
jgruizinga
Jan 2024
Michigan
I've been tasked with adding a 3-wire pressure differential transmitter to a system and drawing up the wiring to an existing PLC board. The transmitter is a Veris PW Series, which is a 3-wire transmitter with a pos., neg., and signal. I'd like to set it up for 4-20mA output, but the existing drawing I have for the card I want to use only has pos. and neg. How is this generally accomplished when I have 3 conductors coming from the transmitter? I could pull power from the cabinet, but then I don't know how to send the signal to the control board.
I understand that this is probably very elementary for many of you, but any help is greatly appreciated. Thanks!
What is the full model number of the transmitter? Some of those transmitters can be used as either 3-wire voltage output or 2-wire 4-20ma.
It's a Veris PWLX04S. The manual says: "Output: 3-wire transmitter; user-selectable 4-20mA/0-5V/0-10V". I didn't see anything in the manual that suggests it can be loop-powered, but I'm obviously not very experienced in instrumentation and controls.
If using 3 or 4 wire transmitter then the analogue input needs to be passive (i.e. no power from the card to the transmitter ) loop powered. 2 wire is where the power is fed via the loop from the card (active).
Here are some examples of each. You should be aware that some controller analog inputs share a single common (-) on all inputs on the I/O card.
Does anyone have experience wiring this type of analog pressure transmitter up? It's 4 wires. 3 blacks and 1 green which I assume is earth...
316
Hi everyone, I need some help I new with omron plc. I using plc CP1L. When I do the program it's good and the plc is function as program. But when...
99
Hi there, Trying to get some ascii serial communications working via RS485 (COMMREQ functions). I have attached our wiring for the COM2...
1,013
What's everyone use for I/O drawings on new installs. I am trying AutoCad Electrical, but can't download it due to a MS Office application running...
1,341
Hi all, I wonder what's the best type of cable to use for RS-485 2 wire + GND That is, Data+, Data- & GND I know that Belden 9841 (not...
1,127