317-6tk13-0ab0 memory card eprom error CPU 317T-2 DP,

we did
 

Attachments

  • Afbeelding van WhatsApp op 2024-02-18 om 23.50.34_3fb07aa1.jpg
    Afbeelding van WhatsApp op 2024-02-18 om 23.50.34_3fb07aa1.jpg
    199 KB · Views: 15
  • Afbeelding van WhatsApp op 2024-02-18 om 23.50.34_45e9d3c8.jpg
    Afbeelding van WhatsApp op 2024-02-18 om 23.50.34_45e9d3c8.jpg
    199 KB · Views: 15
  • Afbeelding van WhatsApp op 2024-02-18 om 23.50.35_f4f2bf06.jpg
    Afbeelding van WhatsApp op 2024-02-18 om 23.50.35_f4f2bf06.jpg
    229.7 KB · Views: 15
  • Afbeelding van WhatsApp op 2024-02-18 om 23.50.36_7d0985ea.jpg
    Afbeelding van WhatsApp op 2024-02-18 om 23.50.36_7d0985ea.jpg
    182.2 KB · Views: 18
  • Afbeelding van WhatsApp op 2024-02-18 om 23.50.36_48dc2f73.jpg
    Afbeelding van WhatsApp op 2024-02-18 om 23.50.36_48dc2f73.jpg
    216.4 KB · Views: 17
The “object has already been deleted “

You get that by just pressing the accessible nodes icon?

What happens if you insert the original mmc in the pg’s prommer?

And then press the icon to read the eprom

What happens?
 
The “object has already been deleted “

You get that by just pressing the accessible nodes icon?

What happens if you insert the original mmc in the pg’s prommer?

And then press the icon to read the eprom

What happens?
we get this empty card
 

Attachments

  • Afbeelding van WhatsApp op 2024-02-19 om 16.05.34_ee1455e8.jpg
    Afbeelding van WhatsApp op 2024-02-19 om 16.05.34_ee1455e8.jpg
    197.5 KB · Views: 11
  • Afbeelding van WhatsApp op 2024-02-19 om 16.05.35_4b42dc9e.jpg
    Afbeelding van WhatsApp op 2024-02-19 om 16.05.35_4b42dc9e.jpg
    173.3 KB · Views: 7
Without any (no Simatic manager project or program in a memory card) program….

You’re out of luck that I can see. Maybe someone else here has an idea
 
Without any (no Simatic manager project or program in a memory card) program….

You’re out of luck that I can see. Maybe someone else here has an idea
i hope so .....anyone experience with this

CPU 317T-2 DP​

and a project or something :)
 
found solution ourself .. simatic manager 5.1 can not communicate with 8mb card. we installed 5.4 and could load new firmware .

put memory card back and working again
 

Similar Topics

Hi, We have ControlLogix installed at my plant with Flex IOs communicating with controller through ControlNet module. Yesterday, while controller...
Replies
0
Views
495
I am working on an older system where they are switching out the weigh in motion scale on a conveyor system from an AP Dataweigh to a Mettler...
Replies
3
Views
1,181
Hi all, Need your recommendation my issue below: I have CPU 317 with 4 racks and 5 siemens drives All of them connected on DP out of the CPU...
Replies
2
Views
1,298
I almost have a complete, basic setup for a shop/learning fixture. I've got a used CPU317-2 DP, a G120C, and some purple hose. I'd like to add...
Replies
20
Views
5,385
I need software to connect to a Yaskawa PLC CP-317/CPU. I have a version of CP-717 Control Pack on an old XP laptop, but would like to have a new...
Replies
1
Views
1,602
Back
Top Bottom