4-20 Analog signal bouncing
hayesfaze
Feb 2011
Traverse City, MI
Hello,
I have micro 1400 with a 1762-if4 card installed. Currently I am only using one channel (4-20ma) hooked to a 0-15 psi transducer. It's a dual pump station with 10hp vfd's driving 2.5 hp motors. I have seperate conduits & plenty of spacing between my cables, but when the drives start my analog signal bounces causing my level to jump by about 3 tenths. Normally this wouldn't be a problem except we are trying to maintain a level in a collection trench & 3 tenths really messes with this. I was advised to try & install a capacitor from my signal return to common. This has worked in the past for me, but I would like further input. Thanks a bunch!
these two wires carring 4-20 ma should be separated from any other ac wires especially the ones for the vfd motor power ( 99% these the ones causing the mutual inductance you facing)
Also make sure the Micrologix PLC is well grounded...the noise could be getting to the backplane, and a good ground should help drain it away from the controller.
Once you have tried all the above you may want to try a filter. Using the cards
configuration or a filter in your logic. See pdf and text below.
Hello I have a analog input signal that is bouncing a bit. The PLC card is a 1769-IF8 I changed the input card filter setting from 60hz to 50hz...
4,882
Hello, I have a compact Logix plc and I have been task with configuring alarms into our SCADA when an Analog signal stops moving. The analog...
253
I'm pretty new to PLC's, so forgive me if I use the wrong terminology and whatnot. We have an issue at work where we have a flow meter that is...
295
I need assistance in the form of some example programs pertaining to analog read and write. Thanks in advance. Sangli
202
Hello folks, Hope everyone is doing well. I am a beginner at working in analog signals with PLC Analog module: 1769-IF4 ( 4 analog inputs ) PLC...
1,358