I am recieving a 4-20Ma signal from a peice of equipment. This signal however has only 14 volts and I am getting nuthin. I am putting into an Allen Bradly flex I/O module. Would a signal Isolator help? Any insight would help.
 
Mr. Stevo said:
I am recieving a 4-20Ma signal from a peice of equipment. This signal however has only 14 volts and I am getting nuthin. I am putting into an Allen Bradly flex I/O module. Would a signal Isolator help? Any insight would help.
Is the module set up for current or voltage?

Typical instrument power supply = 24 VDC
Typical 2-wire transducer needs 10 VDC to operate
24 - 10 = 14 VDC maximum to drive the current signal through the load
Typical maximum load resistance is therefore 14V/0.02A = 700 ohms

Voltage input is high impedance.
Selecting current input typically places a 250 ohm resistor in parallel with the input and the module actually measures 1-5 volts.
 

Similar Topics

Hi all, I'm connecting several 4-20mA sensors together in parallel (only one shown below) The enclosure is ABS plastic with metal backplate DAQ...
Replies
5
Views
274
Problem: Our PLC can only output 4-20mA, but the actuators it needs to control, modulate based on a 0-135Ohm signal. Buying 4 or 8 individual...
Replies
7
Views
276
What's your go to 4-20ma isolator. I've got some 4 wire 4-20ma from several flow meters and scales that I would like to isolate before it gets to...
Replies
10
Views
1,695
Hi, I need to read three 4-20mA signals from a DCS(ABB) in a remote 6 channel analog input module with RS485 modbus port. When I connected...
Replies
2
Views
488
Hello this is my first post. Looking forward to being more involved in this community to learn and hopefully help others. Any help or guidance...
Replies
7
Views
790
Back
Top Bottom