I have a customer with a machine that is physically maced out on I/O. I have 5 Thermocouple inputs that are not used. I need a signal conditioner that will let me take a 4-20Ma signal in and give me a Type J output. Its not a necessity for them it more of a want.
Ive looked and I ASSuME that I'm just missing it. Doe anyone have a solution?
Thanks and hopefully your day is going good
I do not think you will find anything of the sort, but I will be watching just incase this does exist.
It is not possible to change the sensor and just run a Type J thermocouple, I ASSuME?
edit: you would need a signal conditioner that could output 4mA to -8.09mV and 20mA to 69.553mV I believe based off the following chart for type J thermocouple
https://www.thermocoupleinfo.com/type-j-thermocouple.htm
Like all thermocouples, the temperature vs voltage relationship is not linear, therefore, this conversion to type J would cause some error.
+1 for Steve Bailey
What is the cat# of your input module? Some Thermocouple modules have a millivolt input range also.
See pdf for 4 to 20ma to millivolt converter
https://cdn.automationdirect.com/static/specs/fcbiposigcond.pdf
Interesting, I see the 1769-IT6 has the mV range might be useful to remember.
I have used the Spectrum Controls Universal analog input modules in the past 1769SC-IF8, they are nice for a mix of analog/rtd/tc.
edit: fixed IF to IT6
Hi There, I've had a wee look around for answer to this, but I can't find a suitible one, so I thought I'd ask you guys... I would like some...
1,971
Hi all, I'm connecting several 4-20mA sensors together in parallel (only one shown below) The enclosure is ABS plastic with metal backplate DAQ...
279
Problem: Our PLC can only output 4-20mA, but the actuators it needs to control, modulate based on a 0-135Ohm signal. Buying 4 or 8 individual...
281
What's your go to 4-20ma isolator. I've got some 4 wire 4-20ma from several flow meters and scales that I would like to isolate before it gets to...
1,700
Hi, I need to read three 4-20mA signals from a DCS(ABB) in a remote 6 channel analog input module with RS485 modbus port. When I connected...
492