I'm attempting to upgrade a 5/02 AB SLC 500 to a 5/03. However when I stick the 5/03 processor in and attempt to put the processor into run mode I recieve a FAULT (invalid rack configuration).
After speaking to AB about the problem they convinced me the rack was bad. So I went and bought a new rack...only to have the same problem. I also tried to upload a blank program and try it. Same result. Same fault. I am able to see the processor with linx, upload, download, etc. I just can't put the processor into run mode without fault or configure the I/O.
Any ideas?
The way to be certain that your Chassis and I/O configuration is correct is to connect RSLogix 500 to the controller while offline and use the "Read I/O Config" feature.
Does the controller indicate a numeric fault code ? That will help narrow things down.
One other thing... never, ever remove or insert an SLC module under power. You can blow all kinds of components doing that.
I get the "invalid rack config" fault when I'm offline and attempt to 'Read I/O Config". I'll check tomorrow when I'm back at the plant to get the exact fault code.
hello I am getting a 57h fault - Specialty I/O module has not responded to a lock shared memory command within the required limit. Fault randomly...
52
Kindly, we have the following configuration fault on a Kinetix 5700 axis. It only appears when we go online on the Plc. We are just starting the...
95
Have a system that has been running for over a year and all of a sudden getting a ExcessiveVelocityFault on one of the drives when the MSO command...
146
Hi, Experts: We have 20 + years old GE PLC series 90-30 stop running (the run led not on and battery led not on) and HMI showing that "PLC has...
198
Power flex 527 Network based safety drive had faulty and alarm pop up SOS Code internal fault Unable to set or clear the fault manually or...
117